Thread: R404A charge
-
15-02-2008, 05:14 AM #1
R404A charge
R404A must liquid charge.
1) How to liquid charge ?
2) How to know the charge is OK ?
-
15-02-2008, 07:50 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: R404A charge
1. Depends of refrigerant drum type. If it is without tube to the bottom (inside) then you need to turn it upside down. If it is with tube, then in normal position.
Check with sight glass in service manometer that is full with liquid. If you have liquid accumulator charge it in accumulator first and then top up on suction side carefully and with throttling (quick charger or with valve)
2. Charge by weight if it is known. If not, then charge by subcooling and superheat. Simulate low ambient conditions and ensure enough superheat and soubcooling.
Read this:
http://www.mediafire.com/?3xggwmbndxxLast edited by nike123; 15-02-2008 at 07:57 AM.
-
15-02-2008, 08:40 AM #3
Re: R404A charge
Hi Ding Kangzhi,
Better you add one port access for charging and one handvalve on the liquid line, if you want to charge the system while shutdown, just charge in to the port access.
after you start the system and found that the liquid line sight glass has not full yet, so you close the hand valve and top up from the port while the pressure at that side lower than your refrigerant cylinder.
Make sure what is the working pressure that you use.
best regards,
Martua
-
19-02-2008, 04:59 AM #4
Re: R404A charge
Thanks
I am informed that when charging R404A, the compressor can not shutdown, must running the compressor and using sight glass method to charge.
Can you tell me more about charge the sytem while shutdown ? Thanks
-
19-02-2008, 10:52 AM #5
Re: R404A charge
Use only this method ,while shutdown is when your commissioning a new system or your lost the entire gas charge ...and your evacuated the system.While in vacuum & charge to full sightglass.
Overwise , if its screw compressor just put your 60 kg bottle on the suction & let it go.
Recip compressor , you need tread with alittle more caution & watch your discharge temperature ..Plus
too much liquid refrigerant in your sump with an oil pump .You would lose your compressor on oil pressure switch.
I have re -top up 400 kilo systems ,this method on 404a.
-
19-02-2008, 11:54 AM #6
Re: R404A charge
does it have a liquid reciever and sightglass?
Or is a a critcal charge system, ie no liquid reciever?
-
21-02-2008, 02:43 AM #7
-
22-02-2008, 10:31 AM #8
Re: R404A charge
Is it a new installed cold room???
-
24-02-2008, 01:18 AM #9
Re: R404A charge
can anyone tell me what does a pp fault mean on a carel control
-
24-02-2008, 01:33 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
26-02-2008, 02:23 AM #11
-
18-01-2009, 04:31 PM #12
-
05-02-2009, 04:32 PM #13
-
27-12-2010, 03:43 PM #14
Re: R404A charge
Im working in hospital we have Nuaire-86'c freezer with 2 stage compressor.Do you have any idea on how to charge R404,R134A/R508,R134A are they mixed up when charging pls help me?
thanks and more power,
-
27-12-2010, 09:16 PM #15
-
28-12-2010, 03:42 PM #16
Re: R404A charge
you have a cascade system one refrigerant isthe others condensor start with the lest efficient refrigerant and work up these refrigerants are not mixed they are seperate do not mix at any cost all ref should be labelled on machine and watch the very low temp ref they can have high head pressure
Similar Threads
-
To charge or not to charge?
By Fire and Ice in forum Old Refrigeration PhotosReplies: 12Last Post: 20-01-2008, 08:11 PM -
Why not R404a?
By afak in forum Technical SpeculationsReplies: 12Last Post: 02-04-2007, 08:58 PM -
Help please. How to charge a unit
By God55 in forum Air ConditioningReplies: 18Last Post: 23-03-2007, 10:07 AM -
Subcooling vs charge graph?
By Larry2 in forum FundamentalsReplies: 4Last Post: 01-12-2006, 07:40 PM -
Who's in charge?
By chillin out in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-10-2006, 10:51 PM