Results 1 to 13 of 13
    Apr 2007
    canada
    58
    29
    condenser subcooling
    Does load affect condenser subcooling . I know a low condenser subcooling can mean low charge but I work with blast freezers , there is a intial big load and 16 - 20 hours later the load is small . would subcooling be different at the start , when there is a big load and increase as the load gets smaller or would it stay about the same
    NC
    262
    Re: condenser subcooling
    If the the conditioned space is the same temps and outside temp increase....the gas will not condense as fast running through the coil.
    Aug 2007
    Sydney
    52
    1,083
    Yes - As the load drops off the subcooling will increase. Mainly due to the tev closing, reducing evap temp and press, this reduces the amount of refrigerant flow allowing more time to cool the condensing refrigerant.
    Jun 2005
    California
    394
    Tesla is correct, as load deminishes so does the mass flow and condenser has more refrigerant
    Apr 2007
    canada
    58
    29
    From what you guys are saying , to use condenser subcooling to check a possible low charge , there should be little or no load on the system ?
    Jul 2007
    Australia
    1,845
    No, you'd want full load, so it runs optimal when it's needed the most. Check motor amps too.
    The reciever can take care of the excess refrigerant when there's low load.
    Apr 2007
    canada
    58
    29
    Thanks Paul . 10 - 15 degrees subcooling at full load and the sub cooling will increase as the load decreases
    Aug 2007
    Hi Claude11
    Is that in degrees F?
    Apr 2007
    canada
    58
    29
    Is it's degrees F . ( half my equipment is canadian [metric] and half is American made [ standard units]
    Nov 2007
    Romania
    58
    14
    Quote Originally Posted by claude11 View Post
    About subcooling :
    When subcooling the liquid refrigerant before it enters the expansion valve the purpose is twofold:
    - to increase plant refrigeration capacity;
    - to prevent flash gas formation ahead of the
    expansion valve .
    Condensed refrigerant can be subcooled in diferent ways :
    - by dimensioning condensers in such a way that in addition to featuring the necesary condensing surface they also incorporate a subcooling section.In air cooled condensers however the achived effect is normaly insignificant .By expanding the condensig surface you can at best reduce the condensing pressure.
    - by installing internal heat exchangers thereby providing subcooling and suction gas superheating at the same time.
    A good value of subcooling is 3...6 of Celsius degrease.
    Good luck
    Nov 2007
    Romania
    58
    14
    If you have a good condensing control the subcooling it will by ,with small diferences ,the same.
    Nov 2007
    Dubai
    52
    12
    can u provide the full readings and measurments u have.
    Oct 2003
    5,630
    A subcooler incoporated in the condensor coil is not that effective because if flows to the receiver where it will change to its saturated condition.
    It's better to use an additional condensor mounted under the main condensor and where the liquid is coming from the receiver before it goes to the TEV's via an isolated liquid line.
  1. Efficient Water-Source Condenser Design?
    By Enginerd in forum Fundamentals
    Last Post: 28-05-2007, 05:11 AM
  2. Subcooling
    By terryw in forum Supermarket Refrigeration
    Last Post: 07-03-2007, 09:53 AM
  3. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Last Post: 29-04-2006, 02:59 AM
  4. hot discharge air from C.U
    By ong in forum Fundamentals
    Last Post: 29-07-2005, 06:24 AM