    Oct 2021
    Australia
    C02 and chilled water
    Hi all
    I have a chilled water heat exchanger using CO2. On 1 side there is liquid solenoid ICF. Other side is ICS 3 with pilot CVPH and S1 solenoid and S2 CVPH.
    Chilled water is setpoint 5 degrees.
    How would one go about setting the pilots?
    3,364
    Re: C02 and chilled water
    funnyguy,
    Hoping this is a serious request, as sounds unusual to cool water with Co2
    Few ways of doing it, obviously pretty critical on Co2.
    From chart on link below CVP-H range 25 to 52 bar, each turn clockwise is equivalent to 4.1 bar, so starting point could be minimum 5 turns in for 10 deg C.
    25 bar minimum setting on CVP-H, add 5 (turns) x 4,1 bar = 20.1 bar. 25 + 20.1 = 45.1 bar (4510 kpa 10.8 deg C).
    Ensure lots of water flow.
    Accurate gauge
    Relief valve for equipment protection (check setting & equipment maximum pressures).
    Set S2 CVP-H first, EVM solenoid off say 10 deg C or more
    S1 with EVM set second at lower pressure than S2 CVP-H 5 deg C
    0 deg C = 3383 kpa
    5 deg C =3868 kpa
    10 deg C = 4400 kpa
    instrukciya_po_ustanovke_i_nastroike_pilotov_cvp_cvpp_cvc_cve_evm_i_cvh.pdf (danfoss.ru)
    Oct 2021
    Australia
    [/URL]
    Thanks Ranger. I just feel that when I was doing it my gauge needle didn't want to reach 5 deg C (3868 kpa) nor did it want to reach 10 deg C (4400 kpa).
    The ICS module would only want to open at a lower pressure say -5 deg C which I had to leave it at to keep the chilled water system running.
    3,364
    So really it probably should be set to just 1deg C to prevent freezing.
    maybe water flow need to be adjusted to design flow to achieve.
    You can set lower, but risk freezing.
    Do you have design umbers, I would ask if you can.
    Oct 2021
    Australia
    I dont have those. Pity.
    I have had to adjust the chilled water low temperature alarm to prevent system shutdown until reset.
    3,364
    What controls superheat on Co2 side of PHE?
    Is water getting down to temperature?
    Sep 2020
    Australia
    11
    Nothing controls superheat on the shell and tube. It does get down to 5 degree.
    3,364
    So pressure will not increase above water temperature.
    How accurate is gauge, has to be very accurate!
    Adjust S2 as per table of turns if you cannot increase pressure to required opening pressure.
    If there is a power failure & S1 set to low, you may get a freeze up if flooded Co2.
    Is Co2 on shell side