    Re: Current issue

    Quote Originally Posted by nikos_abel View Post
    Hi everybody. Please, look at the readings on the table below:

    Table.JPG

    I was testing a new type of condenser so I took readings to see the behavior in various temperatures.
    The strange thing is that the current is reducing as the ambient temperature is rising.
    I would expect the opposite.

    The refrigerator is a commercial cabinet with 2 doors, the compressor is Tecumseh CAJ4461Y, charged with R134a.


    Hi nicos, fridge is indoor application, then how reached the ambient temperature is 43c.your readings are totally opposite of the logic. Maybe your clamp meter battery is weak………………!

  2. #2
    Join Date
    Mar 2011
    Location
    Greece
    Posts
    12
    Rep Power
    0

    Re: Current issue

    Quote Originally Posted by moideen View Post
    Hi nicos, fridge is indoor application, then how reached the ambient temperature is 43c.your readings are totally opposite of the logic. Maybe your clamp meter battery is weak………………!
    Hi

    The temperature is controlled by me for testing a new condenser to the same circuit.
    Me too was expecting the opposite results, therefore the post!!!!!!

    I have changed the clamp battery and today I will repeat the measurements.

    Thanks everybody