Results 1 to 33 of 33
Thread: Centrifugal chiller.
-
08-01-2012, 09:01 PM #1
Centrifugal chiller.
Hello Mates,
Could someone tell me what the lowest water outlet temperature in a centrifugal chiller is?
-
08-01-2012, 09:03 PM #2
Re: Centrifugal chiller.
what make and model
-
08-01-2012, 09:06 PM #3
-
08-01-2012, 09:17 PM #4
Re: Centrifugal chiller.
depends on the system design/application
-
08-01-2012, 09:19 PM #5
Re: Centrifugal chiller.
Just pure water. How low we can cool water down with a R134A centrifugal chiller?
-
08-01-2012, 09:22 PM #6
Re: Centrifugal chiller.
carrier 19xr Evaporator 19XR Minimum Maximum
Evaporator entering water temperature* °C 6 17
Evaporator leaving water temperature* °C 3.3 10
Condenser (water-cooled) 19XR Minimum Maximum
Condenser entering water temperature* °C 16 35
Condenser leaving water temperature* °C 13.3 44
*
For application requiring brine operation, contact Carrier s.a. for unit selection
-
08-01-2012, 09:24 PM #7
Re: Centrifugal chiller.
Hi
wouldnt try to go lower than 5 degc/.
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
08-01-2012, 09:28 PM #8
Re: Centrifugal chiller.
AS ABOVE
I wouldn't take untreated water below 4-5c as Ice crystals will start to form ,Which could get messy quickly.
Cheers
StuLast edited by stufus; 08-01-2012 at 09:29 PM. Reason: Goshen got there first
Tool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
08-01-2012, 09:28 PM #9
Re: Centrifugal chiller.
york lchmChilled Water Leaving Temperature : R22 & R134a models : 4.0 °C 10 °C
R 407C models : 6.0 °C 10 °C
Chilled Glycol Leaving Temperature : R22 & R134a models : - 6 °C 10 °C
R 407C models : - 2 °C 10 °C
WATER /
Chilled Liquid Temperature Range through Cooler : 3.3 °C 8 °C
GLYCOL
Standard Condenser R22 models : 30 °C 41 °C
SYSTEMS
Liquid Leaving Temperaure : R134a models : 30 °C 55 °C
R407C models : 30 °C 35 °C
-
08-01-2012, 09:30 PM #10
-
08-01-2012, 09:31 PM #11
-
08-01-2012, 09:33 PM #12
-
08-01-2012, 09:37 PM #13
Re: Centrifugal chiller.
not if u add salt! haha
-
08-01-2012, 09:38 PM #14
-
08-01-2012, 09:38 PM #15
-
08-01-2012, 09:39 PM #16
-
08-01-2012, 09:39 PM #17
Re: Centrifugal chiller.
Hi
it is simple as water will freeze at 0 degc, but as said above crystals start to form at 2-3degc
this will lead to evap failure!
wouldnt go there !THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
08-01-2012, 09:43 PM #18
-
08-01-2012, 09:50 PM #19
-
08-01-2012, 10:12 PM #20
Re: Centrifugal chiller.
If you want to go below 5c you need to add a brine/glycol solution if you don't your unit will fail you
Can not get the water below 5 without an evaporation temp of 0c or below. Get yourself a piece of
Copper tube fill it with water seal both ends and put it in a freezer then you will see the results for
Yourself
As mentioned make/model machine is it
-
08-01-2012, 10:25 PM #21
Re: Centrifugal chiller.
Hi Jacek
am with the other members who have replied here... 1*c is way too low
when commissioning i lock out the set point at 6*c and set ice/freeze protection to 4*c
also if evaporating at 1*c the only way the water will reach that temp is if you have no flow !
why do you require 1*c ? what are you cooling and what is the problem ?
chillermanIf the World did not Suck, We would all fall off !
-
08-01-2012, 10:36 PM #22
Re: Centrifugal chiller.
If we maintain the evap temp at +1 deg C, we could get the water temp at 2-3 deg. C (as goshen said). What is the problem? Is it a problem to maintain so low dt between evap temp and water outlet temp?
My question was the general one - how low we could go down with the "pure" water temperature using a ***** chiler...?
-
08-01-2012, 11:01 PM #23
Re: Centrifugal chiller.
Jacek
you need to protect that evap/vessel
so normally you have ice/freeze protection set to 4*c and the low pressure switch set to 0*c
what would you set these to if you lowered the setpoint ?If the World did not Suck, We would all fall off !
-
09-01-2012, 12:44 AM #24
Re: Centrifugal chiller.
You can have close to 0C easily if you use the right evaporator "jester chenson plate" or the like, you can use a closed heat exchanger, shell and tube or plate pack, but extreme care is required. very high water velocities and volumes, super control on suction pressures and a lot of other safeties.
In these case temp drop of water is minimal due to the high flow rates.
-
10-01-2012, 02:58 AM #25
Re: Centrifugal chiller.
a york yk can go to 36 degrees F with smart freeze enabled
-
10-01-2012, 07:31 PM #26
-
10-01-2012, 08:44 PM #27
Re: Centrifugal chiller.
Hi jacek
the specific volume for water will increase at 4c so inlet water temperature should not reach to 4c.
-
10-01-2012, 09:07 PM #28
Re: Centrifugal chiller.
Smart freeze is a York control strategy on the their YK/YS chillers that allows the leaving water temp to be set as low as 2.2c .However programming the parameters to do this needs to be done by someone who knows what they are at.
The software constantly monitors the sensors and temperatures to avoid freeze up.
It's a big song and dance for the sake of 2.5c or a drop of anti freeze.
www.johnsoncontrols.co.uk/...chillers/yk/.../OI-EN-YK.pdf
Cheers
Stu
-
10-01-2012, 09:28 PM #29
Re: Centrifugal chiller.
Why do you want to use pure water as opposed to an anti freeze?
Mostly found in Oxfordshire, UK :)
-
11-01-2012, 08:16 PM #30
Re: Centrifugal chiller.
The general answer for a packaged chiller 'carrier, york, trane' is 6*c
a bespoke system as above would require a 'mad fridgie' supply and fit plus regular tlc from a 'magoo'
if you can supply the flow rates
maybe cost £/$... heat transfer drops and cooling costs rise when anti-freeze is addedIf the World did not Suck, We would all fall off !
-
02-05-2012, 06:21 PM #31
Re: Centrifugal chiller.
Hello,
Could someone tell me what the highest pressure ratio (evaporation temperature/condensing) for a R134a centrifugal chiller? Conditions are, for instance: evaporation temperature = 0-1'C, condensing temperature = "?" (what is the highest possible).
Tnaks in advance for input.
-
28-05-2012, 01:52 PM #32
Re: Centrifugal chiller.
You are talking about the lift and that will be in the design of the chiller.
-
29-05-2012, 12:22 PM #33