Results 1 to 14 of 14
Thread: I am an idiot!
23-01-2011, 02:52 AM #1
I am an idiot!
ok, help. LOL i went out to a customer today to fix a leak in the sight glass flare connection. fixed the leak, vac-ced out and topped up with refrigerant. the room came down to 12 degrees celcius, and i left. got home, and realised i put 507 in it. it is aR22 system, with a r22 TXV, running a kirby WJ26MHG compressor!! must be because it is a sunday, and my brain is fried from the last week. anyway, will it be ok till tomorrow, or does that need to be fixed asap? i wish i had done refrigeration engineering!
23-01-2011, 03:46 AM #2
23-01-2011, 03:48 AM #3
Re: I am an idiot!
Opps, sorry, did not see compressor type. How old is the compressor as these have poe oil. Coldroom only?
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
23-01-2011, 04:08 AM #4
Re: I am an idiot!
it is a fully hermetically sealed unit. the compressor is actually rated for 507/404/22, so i don't think the oil is the problem, more the fact it has a R22 TXV and a number 02 orifice. i am more worried about the suction pressure, as this unit has no t/stat, it is controlled by low pressure control (i hate it when people install them that way). i think i will go back tonight and change the gas over, all under freakin warranty! LOL the joys of business ownership!
23-01-2011, 04:09 AM #5
Re: I am an idiot!
it is 1 month old, i did the comp change just before new years. and yes it is a cool room only, twin fan buffalo trident evap
23-01-2011, 04:15 AM #6
23-01-2011, 04:22 AM #7
Re: I am an idiot!
well.....a little (little!) bit of liquid in the suction line, these compressors have quite a good capacity for liquid charging as the suction port inside is right at the very top of the casing. i have organised with the wife to go and quickly swap out the gas tonight, she can come and brings the kids, we will have tea after somewhere in the city in melb. what a pain! don't you hate it when you do crap like that! i know liquid charging is a no no
23-01-2011, 04:36 AM #8
Re: I am an idiot!
R507 is liquid charge only, so on any 507 systems you will have to do this liquid charging carefully. Kirby units are fine and as you said, can take variety of gasses as all the newer ones are poe oil. No thermostat systems pi** me off, too much tinkering with pressure switch. Difference on R22/R507 suction comparrison is about 110Kpa, 507 will be higher pressure, coldroom will run too cold. Enjoy your night out in the city..Mike
23-01-2011, 04:51 AM #9
Re: I am an idiot!
haha thanks for the help mike, i really appreciate it mate.
23-01-2011, 05:48 PM #10
Re: I am an idiot!
Never used R507 but as it's a R500 gas, therefore an azeotrope, then it could be charged as vapour.
Andy.Health and safety first..........unless I'm in a hurry.
23-01-2011, 06:40 PM #11
23-01-2011, 11:03 PM #12
Re: I am an idiot!
Tayters,Quality, thanks guys. There was some chatter here recently re: R507, liquid or vapour. Suppliers here still maintain the 5 series to be liquid charge, so i've been following their (mis) direction. Next time i'll do vapour. Tayters.. your last avatar was better
...Mike
23-01-2011, 11:17 PM #13
Re: I am an idiot!
Aim to please.
Got a couple more in the bag though!
23-01-2011, 11:46 PM #14
Similar Threads
Idiot of the year
By nike123 in forum Chit Chat & Service StoriesReplies: 1Last Post: 03-03-2009, 02:55 PM -
Idiot test
By frank in forum Chit Chat & Service StoriesReplies: 11Last Post: 23-05-2007, 08:56 PM -
Accidents in Refrigeration and AC world.
By jg/oz in forum RefrigerantsReplies: 32Last Post: 08-05-2005, 08:45 PM -
A refrigeration engineer idiot?
By zolar1 in forum Chit Chat & Service StoriesReplies: 57Last Post: 24-12-2004, 01:43 AM