Thread: P trap correct installation
-
09-03-2010, 04:21 PM #1
P trap correct installation
Hi,
Im currently installing some large DX comms room units.
I have a riser lift of about 8m to 10m, and have been specified to install p traps and oil traps for the remote condenser pipe work.
Can any one specify the correct way of performing this, as several ways have been brought to my attention.
Basically i have a 8 to 10m riser and i would like to know whether i put traps on both discharge and liquid? p traps at the bottom and oil traps half way up??
people are confusing me on the correct way?????
would appreciate some ones advice??
thank you
-
09-03-2010, 05:17 PM #2
Re: P trap correct installation
If you want to get really technical have a look at this pipe guide from McQuay, PDF
http://www.mcquay.com/mcquaybiz/lite...011_120407.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
10-03-2010, 08:18 AM #3
Re: P trap correct installation
Great information Brian, thanks.
-
10-03-2010, 03:38 PM #4
Re: P trap correct installation
Thanks Brian for a useful link.
I saw somewhere[cant remember where], from the bottom of the U trap, 3\8 tube going up to the top of the riser. For my my question how does that help, i was answered that the pressure in the small tube is a bit higher then the large suction pipe and it takes the oil much better up.
Of course a good oil separator is required.
-
10-03-2010, 04:59 PM #5
Re: P trap correct installation
I was told by Emerson for a similar job; traps on discharge pipework at bottom of all rises and 6M intervals.
For example, the system i installed was thus; the pipework ran under computer floor and then up the internal wall for 2M (TRAP INSTALLED AT BOTTOM), pipework exited through wall and ran laterally along wall for 12M where it then ran up the wall (TRAP INSTALLED AT BOTTOM). There was then a rise of 10M to roof level (TRAP INSTALLED 6M FROM BOTTOM).
-
10-03-2010, 05:35 PM #6
Re: P trap correct installation
Hi, simon sheppard
check this link ... maybe you can find some good info for you....
http://www.refrigeration-engineer.co...ead.php?t=4392
also, searching RE forums maybe you can find more information ...
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
10-03-2010, 05:58 PM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: P trap correct installation
While we are at traps, what would be better, trap made of fittings with smallest dimensions as possible like with 2 45° and one 90° elbow or trap made with bending tools with required minimum bending radius? And what are aceptable dimensions?
Is it same for normal and inverted trap at top of riser?
-
10-03-2010, 06:24 PM #8
Re: P trap correct installation
I would have thought that a pulled bend would be better due to the reduction in pressure drop.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-03-2010, 07:10 AM #9
Re: P trap correct installation
Hi Simon I also read in a Trane Manual excerpt where they pointed out that when using unloading compressors you use this double riser system on the discharge line .The larger pipe goes up to the top of the hot gas line through an inverted trap; so that during the low load conditions the oil in this larger riser will not enter into the smaller riser which will be solely carrying the gas flow. I hope this helps !
-
11-03-2010, 08:43 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: P trap correct installation
..............................
Last edited by nike123; 11-03-2010 at 09:04 AM.
-
11-03-2010, 09:05 AM #11
Re: P trap correct installation
.....oooh I see thanks for the correction Nike123
-
11-03-2010, 09:09 AM #12
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: P trap correct installation
It was misunderstanding from my part!
But smaller riser will not carry only gas. It will still carry oil with refrigerant and with sufficient speed at low load condition because trapped oil in P trap act as plug in bigger pipe.
Problem with this is that if it is lot of P traps (and they are not small as possible), high amount of oil is trapped in these P traps during low load condition (and not returning in compressor).
http://books.google.hr/books?id=gniJ...0riser&f=falseLast edited by nike123; 11-03-2010 at 03:30 PM.
-
11-03-2010, 09:23 AM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
11-03-2010, 10:27 AM #14
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: P trap correct installation
I have read somewhere, that with arrangement like this:
oil in trap is better mixed and carried with refrigerant because of turbulence in sudden change in direction with 90° short radius elbow.
Pressure drop could be compensated with bigger lines diameter at horizontal lines.
Also, that way oil in trap is minimal as much as it could be (and cannot be "minimalier") as oppose to this arrangement:
Also, I would like to know equivalent length of standard P traps.Last edited by nike123; 11-03-2010 at 03:26 PM.
-
11-03-2010, 10:18 PM #15
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: P trap correct installation
Here is what I found on that subject:
-
11-03-2010, 10:22 PM #16
Re: P trap correct installation
Good set of images, thanks.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-03-2010, 07:46 PM #17
Re: P trap correct installation
Hi, nike123
really good one, thanks for efforts,
waiting now for original poster
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
12-03-2010, 08:10 PM #18
Re: P trap correct installation
Good info Nike, I will give it a try on my next installation.
Too bad copper is not transparent, I would like to see how it works inside.
Similar Threads
-
The correct way to write CO2.
By nic_f in forum CO2Replies: 5Last Post: 09-02-2009, 07:27 PM -
Installation of NRVS check valves
By Josip in forum NH3Replies: 10Last Post: 02-12-2008, 01:33 PM -
Q: Piping installation for Split Types
By brianubaldo in forum RefrigerantsReplies: 11Last Post: 30-04-2008, 02:23 PM -
how can i correct the dilution of the oil lubricant when i use hydrocarbons?
By mebluna in forum RefrigerantsReplies: 5Last Post: 11-07-2007, 03:06 AM -
Evaporative condenserīs liquid drain trap
By Volnei in forum IndustrialReplies: 7Last Post: 24-10-2003, 02:46 AM