Results 1 to 50 of 896
Thread: AWHP superheat & sub-cooling
Threaded View
-
07-08-2009, 05:56 AM #11
Re: AWHP superheat & sub-cooling
Revised plan of action:
1. Modify partition separating condenser from compressor.
2. Properly insulate condenser & partition walls.
3. Test system response to these changes.
4. Re-position filter drier to vertical orientation.
5. Test system response to this change.
6. Install water regulating valve.
7. Test system response to this change.
8. Adjust WRV & iterate adjustment/testing.Engineering Specialist - Cuprobraze, Nocolok, CD Technology