Results 1 to 12 of 12
Thread: Compression vs Absorption system
-
18-12-2004, 08:16 AM #1
Compression vs Absorption system
can any body give me comparison of the two systems?
plz explain in both financial and technical terms
Regards
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
-
18-12-2004, 09:05 AM #2
Re: Compression vs Absorption system
Originally Posted by abbasi
Cost wise there is huge difference if you compare the compression and absorption type chiller system.(in India Reciprocating type unit of say 100TR costs Rs.1000000.00 and Aborption unit of same capacity will cost Rs.2400000.00)
technically both systems are totally apart compression type require another deivce or drive to drive the compressor.
where as absorption type needs heat source only it may waste heat of foundries, biogas, CNG or steam or even hot water of Elecricity generators( og more than 500MW)
compresion units works with refrigerant only where as absorption units works with refrigerant and absorber.
dunham bush's web site explains all about absorption
Tejbir Singh
Tejbir SinghLast edited by Tejbir Singh; 18-12-2004 at 09:20 AM.
-
02-01-2005, 10:20 PM #3
Re: Compression vs Absorption system
Technicly there are huge differences between the 2 systems :
A compression cycle uses : a compressor (mechanical action is needed) a condenser , an evaporator and an expansion device . . .
The refrigerant used in compression cycles in a full chemical composite that his proprieties varies according to his pressure and tempreture , the cycle takes advance of those propreties to produce cold (no such thing called cold , the cold is the substruction of heat from a place ).
An absorption cycle uses a generator usually need power or a source of heat to heat a solution of Ammonia NH3 or Lithium Bromire L2Br and have a condenser , evaporator and an absorber.
So the refrigerant used here is a water + additives (NH3) wihch makes the solution that will produce cold according to the evolution of it's propreties in the cycle .
Ammonia is very toxic and isn't advised to be used in residence and commerce ... Lithium Bromire isn't toxic , it is used nowadays in the minibars in the hotels rooms (ex: Electrolux minibars) .
Financially an absorption system costs more than a compression one maybe because it is rarely manufactured comparing to the compression systems
Comfort :
Absorption systems are noise free
Compression systems have noises
Servicing :
Absorption can be considered as a static system that rarely needs to be serviced and maintained.
Compression is a dynamic system with moving parts which cause it to need maintenance and servicing periodicly.
Hope the information were useful for uEngineering, sciences, math, physics and my brain will generate "not responding " soon
-
11-11-2008, 09:57 AM #4
Re: Compression vs Absorption system
we should compare compression,absorption & thermo-electric. compressor system is for home & commercial cooling system. absorption is for industrial cooling system. thermo-electric is for small fridge.
-
13-11-2008, 03:27 AM #5
Re: Compression vs Absorption system
compressor system is for home and commercial cooling system?
It is not correct, compression is also for industrial cooling system, and is used widely.
-
17-11-2008, 04:37 AM #6
-
18-12-2008, 02:40 AM #7
Re: Compression vs Absorption system
Compression uses electrical energy Absorption uses heat energy(it can be steam, direct fired, Natural gas etc)
Absorption in todays context is used where you have surplus steam similar to Paper mills where they have Co generation power plants or where easy availabilty of gaseous fuel like LPG or LNG is available.
Absorption is basically combination of heat & Mass transfer and has very few moving parts and will be bulkier compared to compression system.
Heat rejection factor in Compression system is in the order of 1.2 for water cooled system and for Absorption it 1.8 and needs bigger cooling tower compared to Compression system
-
02-02-2009, 08:28 AM #8
Re: Compression vs Absorption system
i know the technical details, i just want financial comparison/feasibility
Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
-
02-02-2009, 08:12 PM #9
Re: Compression vs Absorption system
I would have thought that after four and a bit years you might have the answers by now
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-02-2009, 03:50 PM #10
Re: Compression vs Absorption system
Can you give capacity and fuel source(steam / diesel / CNG /LPG) for Absorption to enable make a comparison.
In any case Absorption is feasible only where surplus steam is available.
For 100 TR Screw Chiller will cost Indian Rs.1800000 , where as Steam fired absorption shall be Rs.2500000 and you need to add boiler cost if captive generation need to be made.Trust this will give you a fair idea.
As per BEE(Bureau of Energy Efficiency) in their reccommendations suggest to use Vapor Absorption only where Steam is available in surplus typically in CO GEN Plants, Paper Mills where steam is used for process and will be available.
-
06-02-2009, 08:26 PM #11
-
06-02-2009, 09:16 PM #12
Re: Compression vs Absorption system
I see its 4 year old but can somebody point in the direction of how an absorbers system works, many thanks
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
absorption system
By rhvac in forum IndustrialReplies: 2Last Post: 22-06-2006, 12:29 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM