    Jul 2005
    28
    Why does one outdoor fan shut off in heat cycle?
    I have two Hitachi 5T heat pumps. Each outdoor unit has two fans. One of these is controlled by a pressure switch and shuts off at times. Why is this? I would think the unit needs all the air possible in order to extract as much heat as possible. Note that this is not the defrost mode when both fans stop.
    Apr 2008
    Southampton, England
    49
    1,023
    36
    Re: Why does one outdoor fan shut off in heat cycle?
    Don't know about the specifics of a Hitachi but older Fujitsu's I seem to recall would do it so as to control the temperature of the indoor coil. If indoor coil was getting too hot (over 60*C roughly) outdoor fan would slow down to reduce capacity then stop if coil temp got to a certain level.
    Cheers,
    Andy.
    Jul 2005
    28
    In this case there is no temperature sensor on the indoor coil. The fan is controlled by a pressure switch on the refrigerant line. I'm not sure if it on the high or low side. I cannot see any reason to shut down one fan except for defrost, when both stop.
    Oct 2001
    Nottingham UK
    5,667
    Quote Originally Posted by JCole21961 View Post
    it's called superheat control