    daikin vrv2 reclaim



    I have a daikin rsey8kly1 outdoor which im changing the inverter comp on.is there a setting so i can drive all the valves in the outdoor on so i can reclaim of the gas.
    Thanks in advance



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: daikin vrv2 reclaim

    Set the condensing unit in to service code 21 to open the valves for reclaiming and vaccing out.
    See this link http://www.refrigeration-engineer.co...ervice-mode-21
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: daikin vrv2 reclaim

    Ballvalve, when was this unit installed and what's exactly the roblem with it?
    VRII or VRVIII?
    Thanks
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin vrv2 reclaim

    R22 VRV doesn't have a vac/reclaim mode, use three port gauges and vac/reclaim form the three lines (liq/Dis/Suct).