Fitting an EPR will mess with TXV as you are putting a false restriction on the suction line, the EPR will open / close to maintain its setting irrespective
al 03-06-2024, 09:01 PMhttps://www.parker.com/content/dam/P...-090/90-20.pdf
Do you have any flow through
Is the sizing of the EPR ok?
Do you have a sight glass you can use to check you have a constant solid liquid supply to the TXV?
SH calculated at the access port at the TXV sensing bulb.
kengineering 02-06-2024, 03:08 PM
Re: Setting EPR and TXV
Thanks for all the idea sharing. Seems we just needed to make very small adjustments and be patient. One of the difficulties I face is working from home