Are you calculating superheat on the evaporator pressure, upstream of EPR valve?
RANGER1 23-05-2024, 10:01 PMCould you apply the correct voltage to the LP switch to test the switch and controls work correctly?
Then trace back the wiring from the switch
What type of expansion valve are you using?
How does the rest of the system look? Subcooling, liquid line sight glass, filters and strainers
Re: Scania Higer 2018
Yes thats a good start, I had 2 coaches this week with the same fault was kind of hoping someone could put there finger on the pulse with the issue as
Coldair98 25-05-2024, 08:38 AM