10-10-2009, 10:41 AM #1
Chiller questions
I saw a component on the refrigerant pipework on a chiller and was told it was an Auto Air Vent, I dont know if thats right, also why would one be necessary if the circuit had been evacuated before gas charge?
Also I think the circuit has a leak in the heat exchanger, what is the best way to be sure? putting a dye in the circuit to see if it goes into the water?
-
10-10-2009, 11:39 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Chiller questions
Auto air vent is on water pipes and not on refrigerant pipes.
There is no way for valve to distinguish refrigerant gas from air. One who told you that is telling you rubbish, or I am lost something in translation.
You probably saw something like this.Last edited by nike123; 11-10-2009 at 05:43 PM.
-
10-10-2009, 01:22 PM #3
-
10-10-2009, 03:39 PM #4
Re: Chiller questions
Thanks for that
-
10-10-2009, 03:40 PM #5
Re: Chiller questions
What about knowing if a leak is in a heat exchanger?
-
10-10-2009, 05:31 PM #6
-
11-10-2009, 03:19 PM #7
Re: Chiller questions
Remove refrigerant, pressurizing system with nitrogen and see if pressure drops and pressure increase on evaporator.
What gas is in it? If you have R22, you can take some water from the evaporator, boil it and put your leak detector (or halid torch) in the fumes. R22 dissolves in the water.
What sort of heat exchanger do you have?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
12-10-2009, 12:06 PM #8
Re: Chiller questions
Thanks for that tip, I like the idea of boiling the water. The chiller is a Carrier with R407c gas, I was thinking to cut the pipework and pressure test the heat exchanger and the rest of the circuit seperately, but surely there are easier methods.
-
12-10-2009, 12:26 PM #9
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
12-10-2009, 09:17 PM #10
Re: Chiller questions
maybe if you close al the automatic vents,or air-separators on the water circuit,and see if the pressure is rising.
Ice
-
12-10-2009, 11:02 PM #11
Re: Chiller questions
What is the model number of your carrier chiller
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM -
Questions about Chiller Design
By Vincent Yu in forum FundamentalsReplies: 9Last Post: 06-06-2008, 01:00 PM