Results 1 to 11 of 11
    Oct 2009
    8
    Chiller questions
    I saw a component on the refrigerant pipework on a chiller and was told it was an Auto Air Vent, I dont know if thats right, also why would one be necessary if the circuit had been evacuated before gas charge?
    Also I think the circuit has a leak in the heat exchanger, what is the best way to be sure? putting a dye in the circuit to see if it goes into the water?
    Split Croatia
    6,106
    7
    30
    Re: Chiller questions
    Auto air vent is on water pipes and not on refrigerant pipes.
    There is no way for valve to distinguish refrigerant gas from air. One who told you that is telling you rubbish, or I am lost something in translation.
    You probably saw something like this.
    Oct 2006
    CORDOBA -ARGENTINA
    69
    69
    12
    Far far away , there where centrifugal R11 chiller , working on Vacuum , so it have AUTO AIR VENT.
    Oct 2009
    8
    Thanks for that
    Oct 2009
    8
    What about knowing if a leak is in a heat exchanger?
    Apr 2009
    israel
    44
    778
    13
    Quote Originally Posted by DEVITG View Post
    not so far away and they are called purge units
    still used on r-123 units!!!
    Oct 2003
    56
    5,519
    28
    Quote Originally Posted by colsy View Post
    Remove refrigerant, pressurizing system with nitrogen and see if pressure drops and pressure increase on evaporator.
    What gas is in it? If you have R22, you can take some water from the evaporator, boil it and put your leak detector (or halid torch) in the fumes. R22 dissolves in the water.
    What sort of heat exchanger do you have?
    Oct 2009
    8
    Thanks for that tip, I like the idea of boiling the water. The chiller is a Carrier with R407c gas, I was thinking to cut the pipework and pressure test the heat exchanger and the rest of the circuit seperately, but surely there are easier methods.
    Split Croatia
    6,106
    7
    30
    That is second easiest method.
    First is lucky find.
    May 2008
    803
    10
    maybe if you close al the automatic vents,or air-separators on the water circuit,and see if the pressure is rising.
    Ice
    Jun 2006
    South Coast
    252
    What is the model number of your carrier chiller
  1. process chiller help
    By talon771 in forum Industrial
    Last Post: 12-01-2011, 08:42 PM
  2. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Last Post: 30-05-2009, 08:31 AM
  3. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Last Post: 06-10-2008, 03:23 PM
  4. Questions about Chiller Design
    By Vincent Yu in forum Fundamentals
    Last Post: 06-06-2008, 01:00 PM