31-08-2017, 01:14 PM #1
Daikin ducted indoor units sweating back
We have a client and his two indoor units are sweating back the outdoor unit is in his garage and the heat his going nowhere the temp in there is 52 degrees would this cause the indoor units to start sweating ? The trouble is there is no where to extract the hot air
-
31-08-2017, 05:47 PM #2
Re: Daikin ducted indoor units sweating back
His garage has walls so there is somewhere to get rid of the heat.
52°C is is way above the design operating conditions I'm sure.Brian, retired in Devon.
-
01-09-2017, 06:34 AM #3
-
05-09-2017, 05:08 PM #4
-
05-09-2017, 08:18 PM #5
Re: Daikin ducted indoor units sweating back
Vent to the underground drive.
Brian, retired in Devon.
-
06-09-2017, 01:19 AM #6
Re: Daikin ducted indoor units sweating back
You have to dump internal heat in place where the refrigerant can turns back in liquid form, otherwise system will not work properly, As mentioned by Mr. Brian arrange to vent it at other level, if possible try to fix a high speed extract fan to remove air from the area.
-
06-09-2017, 07:13 AM #7
-
06-09-2017, 07:15 AM #8
Re: Daikin ducted indoor units sweating back
The underground drive is like another sealed area
-
06-09-2017, 01:15 PM #9
Re: Daikin ducted indoor units sweating back
Is it possible to convert to a water cooled condeser, heat exchanger? No way will it work if you cannot get rid of the heat from the refrigerant, best of luck to you.
-
06-09-2017, 07:27 PM #10
-
06-09-2017, 11:09 PM #11
Re: Daikin ducted indoor units sweating back
Is it possible to upload the building drawing and area snapshoots with units marked on it, may be there a way.
Last edited by malik55; 06-09-2017 at 11:12 PM.
-
07-09-2017, 08:00 AM #12