    Daikin ducted indoor units sweating back
    We have a client and his two indoor units are sweating back the outdoor unit is in his garage and the heat his going nowhere the temp in there is 52 degrees would this cause the indoor units to start sweating ? The trouble is there is no where to extract the hot air
    Sep 2010
    70
    209
    10
    Re: Daikin ducted indoor units sweating back
    His garage has walls so there is somewhere to get rid of the heat.
    52C is is way above the design operating conditions I'm sure.
    Brian, retired in Devon.
    Feb 2008
    Portugal
    47
    201
    11
    Quote Originally Posted by FaultCode View Post
    There is nowhere to take the heat as both sides are garage and the front of garage goes into underground drive
    Dec 2005
    Cheshire
    33
    257
    15
    Quote Originally Posted by eurocooling View Post
    Have you got any pictures? What is behind the rear garage wall?
    Sep 2010
    70
    209
    10
    Vent to the underground drive.
    Mar 2005
    u.a.e
    166
    14
    You have to dump internal heat in place where the refrigerant can turns back in liquid form, otherwise system will not work properly, As mentioned by Mr. Brian arrange to vent it at other level, if possible try to fix a high speed extract fan to remove air from the area.
    Feb 2008
    Portugal
    47
    201
    11
    Quote Originally Posted by Slim R410a View Post
    This is underground garage so it impossible to vent the air
    Feb 2008
    Portugal
    47
    201
    11
    The underground drive is like another sealed area
    Nov 2010
    wales
    9
    Is it possible to convert to a water cooled condeser, heat exchanger? No way will it work if you cannot get rid of the heat from the refrigerant, best of luck to you.
    Feb 2008
    Portugal
    47
    201
    11
    Quote Originally Posted by niceman View Post
    You are correct this was design by a Portugusse builder and work crap
    Mar 2005
    u.a.e
    166
    14
    Is it possible to upload the building drawing and area snapshoots with units marked on it, may be there a way.
    Feb 2008
    Portugal
    47
    201
    11
    Quote Originally Posted by malik55 View Post
    I see see what I can do