With hand held instruments or with the lg software, cable and dongle were the subcool and superheat readings taken during operation before a defrost and then later after a defrost?

I'm just trying to work out where the refrigerant is during operation changes.

If it was R407C then internal fractionation would be a possibility. But with R410A there would be zero fractionation problems.