    Unhappy carrier air curtains



    hi guys ,
    im after some info on operation of air curtains
    ive got to service 67 of them some are working ok some are blowing a gale and i understand from a college that they have bellows inside them to restrict air being supplied to them from air handlers i would appreciate any info, i know the carrier ones i have to work on have an interface and somekind of presure device attected to it , the whole thing is controlled via a bms but lots of rooms are supplied by the same air handler so if you change any temps or fan speeds it affects all of the rooms , ive checked the little pipes that link the interface and presure device and also checked the filter onthe unit would appreciate any help thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: carrier air curtains

    You seem to have checked the first basics.

    What should the volume control be set at and what are they set at?

    Are the pilot holes clear and are the restrictors in place?

    Electronic controls, is the BMS sending the correct signal, has the controller gone belly up?

    You should be able to connect the pressure tubes directly to the bellows bypassing the controls, this will close the bellows and prove that they work.

    More to follow when I remember, it's been a long time.

    edit: You might find this useful from Carrier...
    http://eto.carrier.com/litterature/psd/13716.pdf
    Last edited by Brian_UK; 23-01-2008 at 10:20 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: carrier air curtains

    Paul,
    Is this site near Woking by any chance???

  4. #4
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: carrier air curtains

    no sorry mate its up north

  5. #5
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: carrier air curtains

    thanks brian i will give it a try???

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: carrier air curtains

    Ok,
    Some years ago, I was involved in a site in Woking.
    Similar set up, we also had problem with the bellows not sealing...Turned out that the supplied pressure from the AHU were about 3 times what it should have been.
    Ended up replacing fan motors and installing inverters and new controls, after that we hardly had any problems on site.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier fault codes
    By richelli in forum Trouble Shooting
    Replies: 5
    Last Post: 18-06-2010, 07:35 AM
  3. Carrier Pro Dialog Plus help
    By borodave1973 in forum Air Conditioning
    Replies: 5
    Last Post: 11-11-2007, 06:47 PM
  4. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM
  5. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •