26-01-2005, 11:24 PM #1
Daikin fault codes
Hi there.
Does anyone out there have the fault codes for daikin units
i have no problems so far but i have started to service alot of them lately and would like to have the info if needed nothing worse than the customer asking what it means and you dont no..
Thanks.
-
27-01-2005, 06:34 AM #2
Re: Daikin fault codes
hers some
DAIKIN MALFUNCTION CODES
Code Place Description
AO Indoor Error of external protection device
A1 Indoor PCB defect
A3 Indoor Malfunction of drain Level control system
A5 Indoor Freeze-up prevention
A6 Indoor Fan motor lock, Overload
A7 Indoor Malfunction of swing motor flap
A9 Indoor Malfunction of EEV
AF Indoor Drain level above limit (clogging)
AJ Indoor Malfunction of capacity set device
C3 Indoor Malfunction of drain thermistor
C4 Indoor Malfunction of liquid pipe thermistor
C5 Indoor Malfunction of gas pipe thermistor
C7 Indoor Lower louvre limit switch/motor
C9 Indoor Malfunction of air thermistor
CC Indoor Malfunction of moisture sensor
CA Indoor Malfunction of discharge air thermistor
CJ Indoor Malfunction of remote control thermistor
CE Indoor Malfunction of radiant heat sensor
E0 Outdoor Activation of outdoor safety device
E1 Outdoor PCB defect
E3 Outdoor Activation of high pressure switch
E4 Outdoor Activation of low pressure switch
E5 Outdoor Activation of compressor over heat protection
E5 Outdoor Compressor motor lock
E6 Outdoor Compressor start up error
E6 Outdoor Standard compressor lock/overcurrent
E7 Outdoor Fan motor lock, Overload
E8 Outdoor Inverter input overcurrent
E9 Outdoor Malfunction of EEV
EA Outdoor Four way valve defective.
F3 Outdoor Abnormal discharge pipe temperature
F6 Outdoor Refrigerant overcharged
FC Outdoor Low pressure drop.
H3 Outdoor High pressure switch defect
H4 Outdoor Low pressure switch defect
H6 Outdoor Compressor motor position detection sensor error
H7 Outdoor Fan motor position detection sensor error
H8 Outdoor Current transformer error
H9 Outdoor Malfunction of air thermistor
J1 Outdoor Malfunction of pressure sensor
J2 Outdoor Current sensor malfunction
J3 Outdoor Malfunction of discharge pipe thermistor
J4 Outdoor Low pressure saturation thermistor
J5 Outdoor Malfunction of suction pipe thermistor
J6 Outdoor Malfunction of heat exchanger thermistor
J7 Outdoor Malfunction of heat exchanger liquid thermistor
J8 Outdoor Malfunction of liquid pipe thermistor
J9 Outdoor Malfunction of gas pipe thermistor
JA Outdoor Malfunction of discharge pipe pressure sensor
JC Outdoor Malfunction of suction pipe pressure sensor
JH Outdoor Malfunction of oil temperature sensor
L0 Outdoor Malfunction of inverter
L3 Outdoor Electronic component box overheat
L4 Outdoor Inverter cooling defect
L5 Outdoor Comp motor ground fault, Short circuit
L6 Outdoor Compressor motor grounding/short circuit
L7 Outdoor Total input overcurrent
L8 Outdoor Comp overload, Motor disconnected
L9 Outdoor Compressor lock
LA Outdoor Power unit malfunction
LC Outdoor Transmission between inverter & outdoor
P1 Outdoor Inverter over ripple
P3 Outdoor Thermistor abnormality
P4 Outdoor Power unit humidity sensor malfunction
PJ Outdoor Failure of capacity set resistor
U0 System Shortage of refrigerant or EEV failure
U1 System Negative phase, Open phase
U2 System Power supply insufficient
U3 System Wiring check operation not executed
U3 System Mismatch of indoor and outdoor units (Split only)
U4 System Transmission between indoor units
U5 System Transmission to remote controller
U6 System Malfunction transmission outdoor to BP unit
U7 System Transmission between outdoor units
U7 Outdoor Malfunction between outdoor boards(RMX/RX RK)
U8 System Transmission between master & slave R/C
U9 System Transmission error between indoor to outdoor
UA System Excessive number of fancoils
UC System Address duplication of central controllers
UE System Transmission error between indoor & central
UF System Refrigeration system not set/wiring - piping
UF System Terminals 1 and 3 crossed (Split/Skyair)
UH System System error, Refrigeration system set up
M1 System PCB defect
M8 System Transmission error between central controllers
MA System Improper combination of optional controllers
MC System Address duplication, Improper setting
64 VAM Indoor unit air thermistor error
65 VAM Outside air thermistor error
68 VAM
6A VAM Damper system alarm
6A VAM Damper system and thermistor error
6F VAM Malfunction of remote controller
6H VAM Malfunction of door switch or connector
94 VAM Internal transmission error
Grey fault codes, system still runs, but check ASAP
cheers
richard
-
27-01-2005, 07:58 PM #3
Re: Daikin fault codes
And if you are working on the VRV, here's a link to the centralised controller and fault codes. A handy guide http://www.daikinac.com/pdf/op_manual/DCS302C71.pdf
-
27-01-2005, 11:33 PM #4
Re: Daikin fault codes
Thanks for the codes they will be very handy at least a wont have to stand there looking puzzled if i see them on the screen..
cheers..
-
03-07-2007, 05:21 PM #5
Re: Daikin fault codes
i need some help about Daikin Split unit.I had replace a PCB on the outdoor unit with the same setting which were on the old one ( visual).After starting i got a fault "PJ" ( PJ Outdoor Failure of capacity set resistor ).Can someone tell me how to solve that problem.Thanks in advance.
Last edited by kipetkov; 03-07-2007 at 05:24 PM.
-
03-07-2007, 06:04 PM #6
-
03-07-2007, 06:18 PM #7
Re: Daikin fault codes
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
03-07-2007, 10:10 PM #8
Re: Daikin fault codes
inormally just use the new daikin text service text them the fault code and they reply within seconds excellent or even better ring them if your confused good luck
adam
-
04-07-2007, 05:59 AM #9
Re: Daikin fault codes
THanks for the fast replay.With the PCB have not arrive with a plug i checked few times.The model number is : RYEP100L7W1.Is that mean that i need just to plug it in and it will start working or there is another steps which have to be done? Thanks in Advance.
-
04-07-2007, 06:39 PM #10
Re: Daikin fault codes
Look at the boards side by side, on the original board you will find a plug that's not on the new board (normally it's a plug with a looped cable in it but there are other versions, just a plug with internal short, the cable replaced by a resistor are the ones that springs to mind).
Then just move the plug across.
-
04-07-2007, 08:40 PM #11
-
04-07-2007, 09:01 PM #12
Re: Daikin fault codes
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
05-07-2007, 08:19 PM #13
Re: Daikin fault codes
I checked- nothing.Most probably the company installed has removed them from the unit if there is or the DAIKIN company miss to fit one in the box.
Is that mean that i can just a normal cable to brige it or there is a special resistor in that plug?.Maybe my ? are stupid but DAIKIN are not the one which i use to services them) i dont know nothing about them ).Thanks in advance .
P.s.-if someone can tell me the step by step what i have to do.Friday is the last day.Its in the school with sick childrens.Last edited by kipetkov; 05-07-2007 at 08:23 PM.
-
05-07-2007, 09:25 PM #14
Re: Daikin fault codes
just changed a board on vrv k series, just changed capacity setting / ch setting and worked fine
-
08-07-2007, 08:09 PM #15
Re: Daikin fault codes
-
10-07-2007, 10:28 AM #16
Re: Daikin fault codes
Finaly i went to the supplier and i got the proper plug for the PCB.Now the unit works fine.Thanks to everyone
-
10-07-2007, 07:14 PM #17
Re: Daikin fault codes
Glad the hear that your problem is resolved.
Shame that you were not supplied with the correct parts at the start.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
19-07-2007, 10:16 AM #18
Re: Daikin fault codes
Hi, I have a default code E4:Outdoor Activation of Low Pressure Switch. Can anyone tell me what this means?
-
19-07-2007, 11:04 AM #19
Re: Daikin fault codes
Can someone please help me. Have installed dakin 8kw reverse cycle split sytem in australia. code is U2 Power supply insufficient. Still registers 235 volts. outdoor Fan starts up for about 30 secs then when compressor starts to kick in it shuts down showing u2 fault even though voltage is correct.
-
19-07-2007, 05:01 PM #20
Re: Daikin fault codes
hi frank dont know if anyone else has tried but i cant get to that page from the hyper link!!
is it me?
-
19-07-2007, 06:54 PM #21
Re: Daikin fault codes
Re the U2 error question from AOE
Can someone please help me. Have installed dakin 8kw reverse cycle split sytem in australia. code is U2 Power supply insufficient. Still registers 235 volts. outdoor Fan starts up for about 30 secs then when compressor starts to kick in it shuts down showing u2 fault even though voltage is correct.
Disconnect the lead from the compressor and try and run the system without the compressor.
If it works OK or flag up a different code then reconnect the compressor (after you killed the power) and try to run it again, this time measure the voltage on the terminals of the compressor as it tries to start (Note: Use a good quality meeter, otherwise there is a risk of false readings, see other treads on this matter).
If the voltage by the compressor drop when the compressor is starting then you are looking for a poor connection somewhere. If you get the U2 error when the compressor is disconnected, then you are looking at something with the controls.Last edited by Brian_UK; 19-07-2007 at 08:02 PM. Reason: Added the quote from the originator.
-
19-07-2007, 08:00 PM #22
-
19-07-2007, 08:01 PM #23
-
19-07-2007, 09:16 PM #24
-
19-07-2007, 09:18 PM #25
-
24-11-2007, 12:45 AM #26
-
12-01-2008, 10:45 AM #27
Re: Daikin fault codes
I Have Found That When The Error Code E4 Comes Up Normally On A New Unit(installation) The Remedy To The Fault Is Just By Double Checking That The Prssure Transducer Is Connected Securly As It Does Come Dislodged When You Accidently Brush It With Your Hand After Removing You Gauges From A Vacum I Have Been Caught Out Like That Before
-
25-08-2008, 11:48 AM #28
Re: Daikin fault codes
I have a unit that I personally have not seen, Unit Model = FTXS25D2 with fault code = A6 Fan motor, Lock/Overload. The blades for the fan run freely, no blokages or grating. Should I just replace the part or could it be fixed? Also could anyone offer me the schematic diagram or tell me how easy it is to pull the fan motor out of the unit. The reason I ask is the cliant is not local so I need to prepare in advance and never changed the fan motor in this unit before.
Thank you in advance if anyone can provide me with some info.
Cheers.
-
25-08-2008, 12:11 PM #29
Re: Daikin fault codes
Possible reasons :
1) Faulty fan motor.
2) Faulty indoor unit's P.C.B.
3) Fan motor cable broken or not connected (S1 connector on the P.C.B)..
-
25-08-2008, 02:37 PM #30
Re: Daikin fault codes
Hmm, the unit once switched on calls for the outdoor unit and starts to cool/heat with compressor running and the indoor coil cooling/heating but indoor fan motor dosn't start, 60secs later unit shuts down to protect unit.
Dose this still sound like a PCB Fault and how can I make a check for sure? How can I check the PCB?
-
25-08-2008, 07:01 PM #31
Re: Daikin fault codes
Koy,
This is the service manual for that model, start at page 152 for your A6 fault code.
http://www.daikinac.com/residential/...e%20Manual.pdf
There are other manuals on the Daikin site if you want...
http://www.daikinac.com/residential/...c=docs&page=39Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-09-2008, 08:51 PM #32
Re: Daikin fault codes
Brian the 2 links you have put up are very useful...thanks................but do you know if daikin do a manual (Like your first link) for there FUQ-B range iv had a look around the web and there site's but im unable to find anything like that one ???? any help please thanks
-
03-09-2008, 06:51 AM #33
Re: Daikin fault codes
i may have the book you need, its a pdf, version if you let me have an email address i will email to you.
-
03-09-2008, 09:47 AM #34
Re: Daikin fault codes
I have to say that in my opinion the most likely fault here is that of a failed indoor fan motor capacitor. Value will be between 0.7 and 1.2 microfarad . It will be soldered to the PCB and should be obvious. It is not a difficult job to de-solder and change... You may even be able to attach miniature croc leads and connect a new one first before de-soldering.
Good luck
Trevor
-
03-09-2008, 07:50 PM #35
Re: Daikin fault codes
Thanks davej e-mail address sent
-
05-03-2009, 07:30 AM #36
Re: Daikin fault codes
hi,
u2 means system power insufficient.
-
03-06-2010, 02:25 AM #37
Re: Daikin fault codes
hi, on the daikin i was servicing the F3 code was showing and I stopped the unit because of refrigeration leak which has been fixed now, but it keeps showing F3. does anyone know how to reset the unit? thanks
-
11-08-2010, 05:46 AM #38
Re: Daikin fault codes
We have a 9 year old FTXD50JVEA which has an H6 fault code. Developed identical problem / symptoms under warranty. Compressor wouldn't run, but turned out to be the board. Took 7 visits before they worked it out.
History repeats now, but all personalities and records have gone.
Any thoughts / suggestions?
The engineer is surprised he is getting no output current from the compressor, even if it is not running.
What sort of Mean Time Between Failure (MTBF) are companies like Daikin working on for boards, compressors and fans. We use for heating only, 2 months of the year, and only in the evening, so running only 18 months out of nine years. Are we unlucky or is this normal?
-
09-07-2011, 04:27 PM #39
Re: Daikin fault codes
anybody ever had an F4 fault on a daikin vrv 3 ? any info please ?
-
09-07-2011, 04:59 PM #40
Re: Daikin fault codes
the only thing i found was this
“F4” Outdoor Unit: Humidity alarm
Remote
Controller
DisplayF4
Applicable
Models
RQYQ-PY1
PQEQ-PY1
Method of
Malfunction
DetectionThe condition of the liquid refrigerant returning to the compressor is detected by the
temperature and pressure of any part during the cooling operation.
Malfunction
Decision
Conditions
When the following humidity condition continues for 30 minutes
Supposed
Causes
Faulty suction pipe thermistor
Faulty discharge pipe thermistor
Defect of high pressure sensor
Defect of indoor unit electronic expansion valve
Contamination
-
10-07-2011, 04:19 PM #41
Re: Daikin fault codes
thanks for that. bit of an head scratcher
-
22-10-2011, 12:06 PM #42
Re: Daikin fault codes
hey guys any one got info on DAIKIN RSEYP10K7W1?
-
21-03-2012, 01:14 PM #43
Re: Daikin fault codes
Hey guys any one can help me to fix U4 error code of daikin inverter?
-
21-03-2012, 01:47 PM #44
-
21-03-2012, 08:40 PM #45
Re: Daikin fault codes
start a new thread and quote the model number-and dont post your e mail onsite,members can access it if req in your home page- click on a thread-in this case air conditioning,then click to start a new post-normally members upload manuals via rapidshare
-
21-03-2012, 10:09 PM #46
Similar Threads
-
Panasonic Fault codes
By ronaldo9 in forum Air ConditioningReplies: 31Last Post: 20-02-2011, 08:57 PM -
carrier fault codes
By richelli in forum Trouble ShootingReplies: 5Last Post: 18-06-2010, 07:35 AM -
Daikin fault codes
By Markie in forum Air ConditioningReplies: 16Last Post: 13-01-2009, 01:58 AM -
Chigo Cpa-09co Fault Codes? E4?
By chigosimon in forum Trouble ShootingReplies: 5Last Post: 24-11-2007, 12:46 AM -
MHI, Sanyo & Fuijitsu Complete Fault Codes
By aeb200 in forum Air ConditioningReplies: 1Last Post: 16-11-2005, 01:11 PM