26-11-2006, 06:42 PM #5
Re: Aircon Condenser outside Earthing Equipotential Zone
Modern inverter driven compressors/condensing units cannot be supplied through an RCD.
If you have taken your mains supply from the consumer unit/dist board on a seperate circuit and then taken a PSC reading that falls within the limits I don't see a problem.
The combined neutral/earth goes all the way back to the centre tap of the supply transformer where it is earthed
As far as the plastic isolator within a water pipe that serves an outside tap, I've never heard of this? Can you elaborate?
I feel that the water would act as a current path anyway, so the plastic 'break' would be rendered uselessLast edited by frank; 26-11-2006 at 06:44 PM. Reason: typo