Results 1 to 19 of 19
-
05-06-2006, 07:25 PM #1
how to test the superheat setting value of a thermo expansion valve?
we ask the supplier to give us the expansion valve with required superheat already.
the problem is, how to testify it during incoming check?
-
05-06-2006, 08:21 PM #2
Re: how to test the superheat setting value of a thermo expansion valve?
You can check the setting on the orifice cage if it is a TEV made up from body and power head.
Otherwise you will have to test it when the system is operating.
Tricky name you have, it doesn't run easily off the tongueBrian - Newton Abbot, Devon, UK
Retired March 2015
-
05-06-2006, 08:58 PM #3
Re: how to test the superheat setting value of a thermo expansion valve?
What brand is it?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
05-06-2006, 10:47 PM #4
Re: how to test the superheat setting value of a thermo expansion valve?
Static superheat is normally published on the datasheet as SS= something.
Then if the TXV is adjustable you will be able to reduce or increase the dinamic superheat.
And if the TXV has an equilibrium capillary, then it will also be insensitive to the evaporator pressure drop
-
06-06-2006, 06:12 AM #5
Re: how to test the superheat setting value of a thermo expansion valve?
hi
the TEV is working on specific rang of evaporator KW ,
if you need to have the exact superheat, you can check it while running the system, and readjust the orifice , to match the superheat required by system manufacturer,,
afeef
-
06-06-2006, 04:46 PM #6
Re: how to test the superheat setting value of a thermo expansion valve?
Hi, friends, thanks for reply. but, is there not a way to check before installation?
if check during running, we offcourse can get the value, but, I don't want the test to be made for each equipment. that means wasting time.
-
06-06-2006, 05:25 PM #7
Re: how to test the superheat setting value of a thermo expansion valve?
Originally Posted by 27143721
-
06-06-2006, 06:57 PM #8
Re: how to test the superheat setting value of a thermo expansion valve?
Originally Posted by 27143721Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-06-2006, 11:07 PM #9
Re: how to test the superheat setting value of a thermo expansion valve?
if check during running, we offcourse can get the value, but, I don't want the test to be made for each equipment. that means wasting time.
-
07-06-2006, 12:03 PM #10
Re: how to test the superheat setting value of a thermo expansion valve?
Connect the inlet of the valve to a bottle of nitrogen.(With a regulator of course ).
On the outlet connect a low pressure gauge and a small opening to allow nitrogen to escape.A small pressure vessel would be helpful too.
Place bulb of TEV into container of crushed ice.0 degrees c.
Difference between 0 degrees C and pressure on outlet side converted to a temp for refrigerant you are using is superheat.
-
07-06-2006, 01:28 PM #11
Re: how to test the superheat setting value of a thermo expansion valve?
Hi,
maybe is possible to do that on some other way, like...
yes, depend on brand and type of valve
Best regards,
Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
08-06-2006, 03:34 AM #12
Re: how to test the superheat setting value of a thermo expansion valve?
I think of static pressure as spring pressure. And if I had to measure it, I would be testing the spring pressure. All the other pressures involved in TEV operation are dynamic... Powerhead, equalizing line, outlet and inlet pressures. More than likely a static superheat is one established with a given inlet and outlet pressure possibly compensating for an equalizing line pressure and a given powerhead pressure.
Temprite's advice makes sense to me, considering that.
-
08-06-2006, 03:38 AM #13
Re: how to test the superheat setting value of a thermo expansion valve?
Originally Posted by Temprite
Thanks, I think this is a good idea, I will try it.
Best regards!
-
08-06-2006, 07:14 PM #14
Re: how to test the superheat setting value of a thermo expansion valve?
Total Pressure is defined as the sum of Static Pressure + Velocity Pressure.
Static pressure can be compared to the energy force acting on the outer walls trying to escape and velocity pressure is the pressure produced by the flow of the fluid through the device.
-
08-06-2006, 07:59 PM #15
Re: how to test the superheat setting value of a thermo expansion valve?
Originally Posted by frankIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
08-06-2006, 11:03 PM #16
Re: how to test the superheat setting value of a thermo expansion valve?
Total Pressure is defined as the sum of Static Pressure + Velocity Pressure.
-
11-06-2006, 09:17 AM #17
Re: how to test the superheat setting value of a thermo expansion valve?
If you need to roughly set up TEV during production then calibrate one system vavle at design conditions then strip it apart & measure compression of orifice cage spring (alco danfoss) or adjusting spindle(sporlan) with a vernier & repeat length on other valves. If small vavle then measure turns of adjustment. Better still make sure all systems are correctly commisioned on site to load conditions by qualified engineer.
-
11-06-2006, 04:18 PM #18
Re: how to test the superheat setting value of a thermo expansion valve?
gentlemen
many suppliers in thier catalogues give the size in kwatt output to that orifice of each manufacturer
it really depends upon the application and how it is designed so if it was designed by the supplier of the room things should be right but if you have any doubts and are asking the question here i repectfully suggest you get futher advice and training
-
13-06-2006, 10:30 PM #19
Re: how to test the superheat setting value of a thermo expansion valve?
The method that Temprite posted is pretty much how the superheat is set before the valve leaves the factory. They use usually an automated system, a bath that is carefully controlled, pressure transducers for upstream and downstream pressures, a PLC to read the parameters and turn the bias screw to get the required static superheat, and of course datalogging for the purposes of process control.
I'm in automotive where almost all valves are between 1 ton and 2 ton with 95% being 1.5 ton. The standard orifice size is 0.8mm for these valves. I would think your valve supplier could tell you what orifice size to use for other tonnage.
I would think however that your time would be better spent insuring that their process and quality control is robust. Maybe ask for a plant tour, and ask to see the process they follow?
Regards, Erik
Similar Threads
-
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
expansion valve aint cold
By justinworne in forum Trouble ShootingReplies: 6Last Post: 26-07-2006, 10:52 PM -
I want to find detailed files about ALCO zz thermo expansion valve
By brightfu1 in forum FundamentalsReplies: 2Last Post: 07-09-2005, 03:07 PM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM