    how to test the superheat setting value of a thermo expansion valve?


    we ask the supplier to give us the expansion valve with required superheat already.
    the problem is, how to testify it during incoming check?



  2. #2
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    66
    Posts
    10,045
    Rep Power
    40

    Re: how to test the superheat setting value of a thermo expansion valve?

    You can check the setting on the orifice cage if it is a TEV made up from body and power head.

    Otherwise you will have to test it when the system is operating.

    Tricky name you have, it doesn't run easily off the tongue
    Brian - Torquay, Devon, UK
    I have to stop saying "how stupid can you be?" to my co-workers.
    They're starting to take it as a challenge...

    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    52
    Posts
    5,496
    Rep Power
    22

    Re: how to test the superheat setting value of a thermo expansion valve?

    What brand is it?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    43
    Posts
    2,554
    Rep Power
    14

    Re: how to test the superheat setting value of a thermo expansion valve?

    Static superheat is normally published on the datasheet as SS= something.
    Then if the TXV is adjustable you will be able to reduce or increase the dinamic superheat.
    And if the TXV has an equilibrium capillary, then it will also be insensitive to the evaporator pressure drop

  5. #5
    Join Date
    Aug 2005
    Location
    iraq
    Age
    57
    Posts
    131
    Rep Power
    9

    Re: how to test the superheat setting value of a thermo expansion valve?

    hi
    the TEV is working on specific rang of evaporator KW ,
    if you need to have the exact superheat, you can check it while running the system, and readjust the orifice , to match the superheat required by system manufacturer,,

    afeef

  6. #6
    Join Date
    May 2006
    Location
    China
    Posts
    18
    Rep Power
    0

    Re: how to test the superheat setting value of a thermo expansion valve?

    Hi, friends, thanks for reply. but, is there not a way to check before installation?

    if check during running, we offcourse can get the value, but, I don't want the test to be made for each equipment. that means wasting time.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    43
    Posts
    2,554
    Rep Power
    14

    Re: how to test the superheat setting value of a thermo expansion valve?

    Quote Originally Posted by 27143721
    Hi, friends, thanks for reply. but, is there not a way to check before installation?
    Yes, read the data sheet of that valve.

  8. #8
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    66
    Posts
    10,045
    Rep Power
    40

    Re: how to test the superheat setting value of a thermo expansion valve?

    Quote Originally Posted by 27143721
    Hi, friends, thanks for reply. but, is there not a way to check before installation?

    if check during running, we offcourse can get the value, but, I don't want the test to be made for each equipment. that means wasting time.
    Some details of the valve you propose using would help get a more informed reply.
    Brian - Torquay, Devon, UK
    I have to stop saying "how stupid can you be?" to my co-workers.
    They're starting to take it as a challenge...

    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,697
    Rep Power
    28

    Re: how to test the superheat setting value of a thermo expansion valve?

    if check during running, we offcourse can get the value, but, I don't want the test to be made for each equipment. that means wasting time.
    Well, if you do manage to find a way of short circuiting the process of correctly setting up a fridge circuit then I'm sure we would all appreciate the info as it would save us all a load of cash
    I'm back on the Pale

  10. #10
    Join Date
    Dec 2004
    Location
    Australia
    Age
    42
    Posts
    522
    Rep Power
    10

    Re: how to test the superheat setting value of a thermo expansion valve?

    Connect the inlet of the valve to a bottle of nitrogen.(With a regulator of course ).
    On the outlet connect a low pressure gauge and a small opening to allow nitrogen to escape.A small pressure vessel would be helpful too.
    Place bulb of TEV into container of crushed ice.0 degrees c.
    Difference between 0 degrees C and pressure on outlet side converted to a temp for refrigerant you are using is superheat.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    58
    Posts
    1,937
    Rep Power
    14

    Re: how to test the superheat setting value of a thermo expansion valve?

    Hi,

    maybe is possible to do that on some other way, like...

    yes, depend on brand and type of valve

    Best regards,

    Josip
    Attached Files Attached Files

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,091
    Rep Power
    15

    Re: how to test the superheat setting value of a thermo expansion valve?

    I think of static pressure as spring pressure. And if I had to measure it, I would be testing the spring pressure. All the other pressures involved in TEV operation are dynamic... Powerhead, equalizing line, outlet and inlet pressures. More than likely a static superheat is one established with a given inlet and outlet pressure possibly compensating for an equalizing line pressure and a given powerhead pressure.

    Temprite's advice makes sense to me, considering that.

  13. #13
    Join Date
    May 2006
    Location
    China
    Posts
    18
    Rep Power
    0

    Re: how to test the superheat setting value of a thermo expansion valve?

    Quote Originally Posted by Temprite
    Connect the inlet of the valve to a bottle of nitrogen.(With a regulator of course ).
    On the outlet connect a low pressure gauge and a small opening to allow nitrogen to escape.A small pressure vessel would be helpful too.
    Place bulb of TEV into container of crushed ice.0 degrees c.
    Difference between 0 degrees C and pressure on outlet side converted to a temp for refrigerant you are using is superheat.

    Thanks, I think this is a good idea, I will try it.

    Best regards!

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    4,697
    Rep Power
    28

    Re: how to test the superheat setting value of a thermo expansion valve?

    Total Pressure is defined as the sum of Static Pressure + Velocity Pressure.

    Static pressure can be compared to the energy force acting on the outer walls trying to escape and velocity pressure is the pressure produced by the flow of the fluid through the device.
    I'm back on the Pale

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    52
    Posts
    5,496
    Rep Power
    22

    Re: how to test the superheat setting value of a thermo expansion valve?

    Quote Originally Posted by frank
    Total Pressure is defined as the sum of Static Pressure + Velocity Pressure.

    ... is the pressure produced by the flow of the fluid through the device.
    It's the pressure generated when the flow is sudden complete stopped.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,091
    Rep Power
    15

    Re: how to test the superheat setting value of a thermo expansion valve?

    Total Pressure is defined as the sum of Static Pressure + Velocity Pressure.
    Of course. My bad. I meant "static superheat" Not Pressure.

  17. #17
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    42
    Posts
    35
    Rep Power
    0

    Re: how to test the superheat setting value of a thermo expansion valve?

    If you need to roughly set up TEV during production then calibrate one system vavle at design conditions then strip it apart & measure compression of orifice cage spring (alco danfoss) or adjusting spindle(sporlan) with a vernier & repeat length on other valves. If small vavle then measure turns of adjustment. Better still make sure all systems are correctly commisioned on site to load conditions by qualified engineer.

  18. #18
    Join Date
    Jun 2003
    Location
    northampton
    Posts
    21
    Rep Power
    0

    Re: how to test the superheat setting value of a thermo expansion valve?

    gentlemen

    many suppliers in thier catalogues give the size in kwatt output to that orifice of each manufacturer

    it really depends upon the application and how it is designed so if it was designed by the supplier of the room things should be right but if you have any doubts and are asking the question here i repectfully suggest you get futher advice and training

  19. #19
    Join Date
    Jul 2005
    Location
    Detroit,USA
    Age
    43
    Posts
    31
    Rep Power
    0

    Re: how to test the superheat setting value of a thermo expansion valve?

    The method that Temprite posted is pretty much how the superheat is set before the valve leaves the factory. They use usually an automated system, a bath that is carefully controlled, pressure transducers for upstream and downstream pressures, a PLC to read the parameters and turn the bias screw to get the required static superheat, and of course datalogging for the purposes of process control.

    I'm in automotive where almost all valves are between 1 ton and 2 ton with 95% being 1.5 ton. The standard orifice size is 0.8mm for these valves. I would think your valve supplier could tell you what orifice size to use for other tonnage.

    I would think however that your time would be better spent insuring that their process and quality control is robust. Maybe ask for a plant tour, and ask to see the process they follow?

    Regards, Erik

Similar Threads

  1. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 03:11 AM
  2. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  3. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  4. Replies: 2
    Last Post: 07-09-2005, 03:07 PM
  5. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Replies: 5
    Last Post: 20-11-2003, 02:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •