09-12-2016, 04:09 AM #1
Daikin mono bloc 16kw for just radiators
Can any one help we just need to heat the radiators up to 40 can we just put this on to the old existing system we do not need to do hot water do we need a tank with this ? Or can it go straight on to the return and flow the system is going on to a house in the algarve Portugal and is used for 8 weeks of the year
09-12-2016, 12:10 PM #2
Re: Daikin mono bloc 16kw for just radiators
Provided that you have thoroughly flushed the system to remove any debris, you could use the mono block to provide heating input only.
Probably best to install an inline filter such as the Fernox TF1 to provide extra filtration for the water circuit.
If the unit is going to be turned off in the cold weather then it would be best to use a special heat pump antifreeze solution such as Fernox HP-5C to a suitable protection level..
You would be able to achieve a maximum flow temperature of 55 degrees, if needed.
Obviously the system would be much more efficient at the lower flow temperatures.
There is no need to have a hot water tank as you can set the system up in a heating only mode.
You can then control the unit by a remote thermostat across terminals 1 & 4 and preset the flow temperature or have it weather compensated.Mobile A/C at its best, see avatar.
10-12-2016, 05:50 AM #3
Thank you for your help
10-12-2016, 11:08 PM #4
If not already fitted, install automatic air bleeders at highest point of water circuit. Will stop all banging and clanging in the pipework.
14-12-2016, 04:42 PM #5
They have been fitted thank you Magoo
15-12-2016, 01:04 PM #6
If your existing system is 'Vented' type (expansion tank in the loft) and you change to 'Unvented', (pressurised) you may end up with a few leaks
