    Daikin mono bloc 16kw for just radiators
    Can any one help we just need to heat the radiators up to 40 can we just put this on to the old existing system we do not need to do hot water do we need a tank with this ? Or can it go straight on to the return and flow the system is going on to a house in the algarve Portugal and is used for 8 weeks of the year
    Dec 2008
    511
    Re: Daikin mono bloc 16kw for just radiators
    Provided that you have thoroughly flushed the system to remove any debris, you could use the mono block to provide heating input only.
    Probably best to install an inline filter such as the Fernox TF1 to provide extra filtration for the water circuit.
    If the unit is going to be turned off in the cold weather then it would be best to use a special heat pump antifreeze solution such as Fernox HP-5C to a suitable protection level..
    You would be able to achieve a maximum flow temperature of 55 degrees, if needed.
    Obviously the system would be much more efficient at the lower flow temperatures.
    There is no need to have a hot water tank as you can set the system up in a heating only mode.
    You can then control the unit by a remote thermostat across terminals 1 & 4 and preset the flow temperature or have it weather compensated.
    Feb 2008
    Portugal
    47
    201
    11
    Thank you for your help
    Auckland
    68
    3,362
    32
    If not already fitted, install automatic air bleeders at highest point of water circuit. Will stop all banging and clanging in the pipework.
    Feb 2008
    Portugal
    47
    201
    11
    They have been fitted thank you Magoo
    Oct 2001
    Nottingham UK
    5,127
    42
    If your existing system is 'Vented' type (expansion tank in the loft) and you change to 'Unvented', (pressurised) you may end up with a few leaks