29-09-2016, 09:09 PM #1
30-09-2016, 10:25 AM #2
Re: Energy balance in evaporator. Thermal load and heat transfer rate
That's correct. Beside the language error (I meant volume flow), due to water's density close to 1, and also the specific heat of water, you "can" round it to the given rule of thumb (term which I understand is a quick and not 100% exact rule to calculate something). Of course chillers work with water+glycol usually, so mix's density isn't 1, neither is the specific heat. So you can use this rule of thumb with fluids whose characteristics are similar to water's.