    May 2009
    uk
    13
    Unhappy PURY-P250YGM-A 1102 fault
    1102 fault driving me mental
    PURY-P250YGM-A
    Indoor units gutted and clean until they shine
    Outdoor unit gutted and cleaned
    correct gas charge in unit
    1102 now appears and then 1302
    compressor going to 112 deg c then ramps down to 75 deg c then up to 112 again (heating)
    any advice?
    May 2012
    1,528
    Re: PURY-P250YGM-A 1102 fault
    Quote Originally Posted by spamfish View Post
    PURY-P250YGM-A
    any advice?
    Don't Gut and Clean em...................
    Rob
    Mar 2008
    Manchester
    33
    Check inddor fileter n non condensibles
    The moving finger writes and leaves a broken fingernail behind!
    5,667
    The compressor is going into protection mode due to the high discharge temp. It's a typical sign of overheating and if you don't address it you will lose the compressor.
    I would check the oil level in the compressor with an infra red thermometer. If it's low then add a little oil into the suction line
    Aug 2009
    Dartford
    88
    Is this in heating mode? I would check LEV 3 in the BC box. undo it to see if it's stuck