    Smile R-410a Gauge Pressure
    I am new to R-410a. Please can anyone tell what are the low & high side gauge pressures for a certain ambient temperature of a domestic airconditioner with R410a.
    Thanks in advance
    5,667
    Re: R-410a Gauge Pressure
    Quote Originally Posted by Mr.Sark
    Thanks in advance
    Try this link http://www.robinair.com/acsolutions/.../presstemp.php
    Mr.Sark's Avatar
    Mr.Sark Guest
    Thanks Frank for replying, chart was very useful, but a domestic unit with R-410a, what is its design pressure? E.g With R-22 its Lowside 4bars & Highside 16 bars with an ambient temperature of 32deg C.
    May 2004
    Scotland
    52
    4
    With r410a on a heat pump split, the gauges are only useful for telling you if you have gas in the system or not, you cant tell the ambient temp by your gauges pressure on R410a i'm afraid.
    cheers
    Surely the manufacturers are the people to advise you of that. The pressures are dependant on the ambient temperatures so will vary.
    If you have a copy of the R410a pressure temperature chart, as provided by Frank, then you should be able to work out the pressures relating to the temperatures that you have measured.
    Oct 2005
    preston lancashire
    12
    without sounding rude u should have some training on 410 also gauge connections r differrent
    Sep 2005
    Slovakia
    Roughly said, split with R410A could be normal
    LP - 8-10 bar
    HP - 25-30 bar
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Mr.Sark,
    I don't think that there is such a thing as design pressure,
    The unit is designed to maintain the evaporating temp above the freezing point,
    It is done by adjusting the outdoor fan to the coil temp, regardless if its cooling or heating, assuming the system is charged as it should be.
    only in sophisticated controls such as VRV and stuff, pressure is being monitored.
    all th splits measure temps:
    indoor temp,
    indoor coil,
    outdoor temp,
    outdoor coil,
    The rest is done by the controller.
    410 is simply another refrigerant.
    You will have to make sure though, that the copper tubing you use, will hold the higher pressure.
    Hope I solved some of the mysteries.
    Chemi
    katyalrk's Avatar
    katyalrk Guest
    while on 410 a can u suggest thickness of copper tubes to hold the pressure?
    5,667
    Quote Originally Posted by katyalrk
    I think I've posted this link before http://www.kembla.com.au/pdf/R410a-V5.PDF
    Apr 2001
    2,099
    27
    Hope you " satisfied" this time
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
    richard hall's Avatar
    richard hall Guest
    on the subject of r410 i know you are supposed to pressure test with nitro to 1.5x d.p is it the same for r410 given the fact that it has higher d.p and therefore may find the smallest weakness?>
    Richard, a strength test is a strength test regardless of the medium used.
  1. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Last Post: 08-03-2007, 05:34 AM
  2. Building a wine cabinet
    By Rory in forum Technical Discussions
    Last Post: 13-07-2004, 08:28 PM
  3. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Last Post: 06-12-2002, 05:11 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Last Post: 16-07-2002, 02:10 PM