23-06-2005, 12:11 PM #1
Cooling condenser of split with condensate from evaporator
Hi,
Would pumping condensate over the fins of the condenser in a split air conditioner result in a worthwhile improvement in efficiency?
I'd have thought it would lower the pressure in the condenser and in turn help the compressor to pump more refrigerant vapour and lower the vacuum in the evaporator too.
Also is the condensate likely to corrode the evaporator? I'd have thought not as it's basically distilled water, if the split is a heat pump the condenser in the outdoor unit will be designed to cope with condensate too.
cheers,
Pete.
-
23-06-2005, 01:58 PM #2
Re: Cooling condenser of split with condensate from evaporator
I would say not worthwhile increase in efficiency, but it wont hurt matters.........
Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
-
23-06-2005, 03:06 PM #3
Re: Cooling condenser of split with condensate from evaporator
The condensate water will rut the steel on the out door unit.
Do not do it. You will gain nothing.
Chemi
-
23-06-2005, 07:30 PM #4
Re: Cooling condenser of split with condensate from evaporator
Would pumping condensate over the fins of the condenser in a split air conditioner result in a worthwhile improvement in efficiency?
I'd have thought it would lower the pressure in the condenser[
and lower the vacuum in the evaporator
Also is the condensate likely to corrode the evaporator?
if the split is a heat pump
The problem with using water to cool the condenser is mostly related to Legionella. The water not evaporated tends to collect in a pool below the condenser coil and in certain circumstances Legionella spores can be circulated by the condenser fan.
Is it worth the hassel?Last edited by frank; 23-06-2005 at 07:32 PM.
-
24-06-2005, 11:11 AM #5
Re: Cooling condenser of split with condensate from evaporator
Originally Posted by frank
Originally Posted by frank
So lowering pressure in the condenser would allow the compressor to pump more refrigerant vapour, in turn lowering pressure in the evaporator.
Still the cooling depends on the amount of liquid refrigerant going through the capilliary/expansion valve, so would the above increase this?
Originally Posted by frank
Originally Posted by frank
cheers,
Pete.
-
24-06-2005, 08:52 PM #6
Re: Cooling condenser of split with condensate from evaporator
Some Airconditioners are actually designed for this.
They can be recognized bij a connection on the side of the bottom tray of the condesing unit end the fan is fitted with a ring on the edges op the fanblades.
This ring picks up the water en spray it on to the condensor.
It has a big effect on the capacity.
With extreem hot weather like past days it is a difference of a blazing hot liquid line or a reasonable cold liquid line.
The condensor should not be soaked with water but just lightly moist.
If you want to try it out, take a whatever condensor of a small unit, connect your gauges, take a spraying flask, take the pressure readings, spray some water on the condensor and see how the pressure lowers.
Victor
-
24-06-2005, 09:00 PM #7
Re: Cooling condenser of split with condensate from evaporator
True, although problems only occur when the bacteria is 'aerosolised' such as in a cooling tower, shower head or even peat dust(!). Evaporative coolers could cause problems with legionella but have a history of safety as the water is not turned into a spray.
The water that is "misted" onto an evaporative condenser usually passes through some sort of water treatment process to kill the bacteria (mostly UV light) but it is the water that collects under the coil, either in the drain pan or on the floor that "ponds" and that can be the cause of Legionella. This needs to be treated as well.Last edited by frank; 24-06-2005 at 09:02 PM.
-
24-06-2005, 09:08 PM #8
Re: Cooling condenser of split with condensate from evaporator
Still the cooling depends on the amount of liquid refrigerant going through the capilliary/expansion valve, so would the above increase this?
-
25-06-2005, 12:04 AM #9
Re: Cooling condenser of split with condensate from evaporator
All window rattlers are designed with slinger rings on the condenser fan and condensers are sized accordingly
Unless in a particulary hot climate the addition of water to a clean condenser on a modern 'japanese' type split is totally unncessary -most in the UK are over condensing enough already- as they are all designed to 46 deg'c operation.
The addition of water on an already over efficient condenser will lower the refrigerant pressure/flow, reducing capacity and increase the chance of icing on the evaparator.
This is why most splits need F.S.C for comms rooms etc during winter
Don't do it...don't bother........
Cheers
Richard
-
26-06-2005, 09:25 PM #10
Re: Cooling condenser of split with condensate from evaporator
Hi,
Thanks for the replies.
So it looks like cooling the condenser would increase the enthalpy of the refrigerant, but will also reduce the capacity of the system in a conventional split as the pressure forcing refrigerant through the capilliary will be lower.
I expect the newer 'inverter' splits with a linear expansion valve might benefit though.
Also trickling the water over the coil for adiabatic cooling instead of spraying it would give less potential for problems with Legionella.
cheers,
Pete.
-
27-06-2005, 07:08 PM #11
Re: Cooling condenser of split with condensate from evaporator
Originally Posted by smileypete
WORTH EXPERIMENTING , not to use , if not designed for moist spray, time pass.
beni joseph,
-
10-07-2005, 08:21 AM #12
Re: Cooling condenser of split with condensate from evaporator
Originally Posted by smileypete
If the ambient temp is high enough for the system to require the condense to be discharged onto the condenser unit then it will surely evaporate before any bacteria can cause a problem.
Also heat pumps produce water in heating mode so provision is made for water to drain away, thus removing the chance of water build up & growth of bacteria.
If the ambient temp is below 30c then there is no need for the condense to be directed onto the condenser, but could in theory aid in high temps providing that the flow was of a suitable level. More than likely it will not be great enough to have any noticeable effect.:cool: Do the job once & do it right. :cool:
Similar Threads
-
Condensor split temperature
By Peter_1 in forum FundamentalsReplies: 14Last Post: 31-07-2011, 05:49 PM -
Evaporative Condenser in reverse cycle
By Friobernal in forum IndustrialReplies: 6Last Post: 16-04-2009, 02:06 PM -
How to controll Logarithmic Mean Temperature of evaporator
By Josip in forum Technical SpeculationsReplies: 14Last Post: 19-08-2006, 12:15 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum IndustrialReplies: 5Last Post: 14-10-2005, 06:34 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum FundamentalsReplies: 0Last Post: 13-10-2005, 05:14 AM