03-01-2011, 07:09 PM #5
Re: 5 ton kws
Sounds about right - the unit is probably not running at design full load. The numbers are about where we would expect them to be with the unit running say 70 to 80% Loaded - meaning the return air and outdoor air enthalpy's are low enough to, in a combined fashion, amount to less that full design load conditions.