    5 ton kws
    Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?
    70
    10,627
    52
    Re: 5 ton kws
    Sorry, don't know.
    What does the data plate on the unit say?
    Jun 2010
    Belize
    11
    Re: 5 ton kws
    there is no refrence to the power consumption , but its a five ton single , 208 volts unit, compressor running and evap fan on high
    Nov 2010
    London
    625
    9
    Re: 5 ton kws
    Quote Originally Posted by ostaine View Post
    Sounds about right - the unit is probably not running at design full load. The numbers are about where we would expect them to be with the unit running say 70 to 80% Loaded - meaning the return air and outdoor air enthalpy's are low enough to, in a combined fashion, amount to less that full design load conditions.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
    Jun 2010
    Belize
    11
    Re: 5 ton kws
    Waiting for a warm day to do recording of with reps from utility company using Fluke test gear. will also record ambient and room temp
    Jun 2010
    Belize
    11
    Re: 5 ton kws
    single 5ton a/c , compressor running, condenser fan running, evap fan on high,
    Ambient 88.5 F
    Power consumption 4.352 Kw
    Room Temp 71.6 F
    Jun 2010
    Belize
    11
    Re: 5 ton kws
    Here's what on the nameplates.
    Condensing Unit
    Make : Goodman
    Model : CKL60 - 1L
    A/C Volts : 208/230 phase 1 Hertzs 60
    Factory Charge oz R22 115
    COMPRESSOR
    Make : Copeland ZR57KC-PFV-250
    RLA 25 A LRA 150
    Evaporator
    Model #UG060CKA2LACL2
    SERIAL # 50050072-4118
    Jun 2010
    Belize
    11
    Re: 5 ton kws
    Condensing Unit
    Make : Goodman
    Model : CKL60 - 1L
    COMPRESSOR
    RLA 25 A LRA 150
    Evaporator