    Re: LG Multisplit ongoing issue... slowly getting there I think!

    Paid £400 for reclaim, (no refrigerant loss whatsoever just slightly undercharged) so unit has exact refrirgerant weighed in as per LG.

    However issues are still exactly the same. No change so I am not very happy.

    WHen the system works it works very well however the next cycle on it may be very poor and air offs will be poor.

    FOr example the other day when it was -2C outside an hour before I was getting air offs of 41C then an hour later air offs were 28C with no change if I put the set point upto 30C.

    So I am back onto LG to see where they are going to take this next.

    I still think its the EEV's as the outdoor unit main header pipe has higher temps than what gets to the indoor units. So its almost like the EEV's are not allowing enough gas through.
    Last edited by back2space; 04-12-2010 at 11:39 PM.

Similar Threads

  1. Daikin output overcurrent issue
    By wilson77 in forum Air Conditioning
    Replies: 15
    Last Post: 18-01-2010, 11:36 PM
  2. Ongoing problem with Fuji ASTA12LLC
    By Seiko in forum Air Conditioning
    Replies: 0
    Last Post: 03-11-2009, 02:51 AM
  3. Beko Fridge freezer - freezer temp issue
    By lukas989 in forum Domestic
    Replies: 2
    Last Post: 30-09-2009, 05:29 PM
  4. Samsung Home Aircon Issue - Display Flashing
    By dazzak in forum Air Conditioning
    Replies: 1
    Last Post: 03-07-2009, 05:05 PM
  5. Flood back issue?
    By Arc in forum Trouble Shooting
    Replies: 15
    Last Post: 28-10-2008, 03:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •