Results 1 to 6 of 6
Thread: rhoss error
-
30-06-2010, 08:33 PM #1
rhoss error
hi everybody
im new in this forum
im having e problem with e rhoss chiller CWA\E 70
here is the situation . the unit has 4 compressors and only 2 are running and on display gives E 22 error
anyone any idea what s going wrong
thanks in advance
-
01-07-2010, 04:52 PM #2
Re: rhoss error
I'd start with the basics. Manufacturer data should tell you what error 22 might indicate, then check those first. Next I'd check for voltages at the contactor and contactor coils.
-
02-07-2010, 05:46 AM #3
Re: rhoss error
check for high or low pressure on that circuit.
Ice
-
03-07-2010, 08:54 PM #4
Re: rhoss error
thank you guys for your suggestions i really appreciate this but i think im gonna need e rhoss manual for cwa/e 70 model . has it anybody
thanks again
-
05-09-2011, 12:30 PM #5
Re: rhoss error
Low pressure circuit 2
-
06-09-2011, 10:38 AM #6
Re: rhoss error
Indeed LP for Circuit 2 and you need to switch off power to the controller to reset this.
Lack of gas (don't overcharge because there's no receiver) or lack of load or TEV fault.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
shining fault codes
By al in forum Air ConditioningReplies: 3Last Post: 17-07-2010, 08:34 AM -
Daikin BRC1C51 Error code help
By monners in forum Trouble ShootingReplies: 1Last Post: 02-11-2009, 11:03 PM -
which compressor is the best?
By cakabo28 in forum New TechnologiesReplies: 33Last Post: 19-08-2009, 06:44 PM -
Angelopo Sm2l Error E2 Please Info About This Error
By CHARLIEZOLO in forum CommercialReplies: 0Last Post: 22-12-2005, 03:47 AM