31-12-2009, 08:17 PM #1
Mitsubishi Mr.Slim heat pump
Hi everyone
I have a Mitsubishi Mr.Slim heat pump 15 000 BTU
i am trying to find specs on it that mention it's minimum outside temperature shut off point cause mine shuts off at -10 celcius and i am wondering if making it shut off at let say -15 would damage it?
I have put it's sensor inside the box (where it is a bit warm) instead of outside, now all i have to do is keep a eye on it and see at what temp. it will shut off.
Thanks
-
31-12-2009, 10:02 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
31-12-2009, 10:37 PM #3
-
31-12-2009, 11:14 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-01-2010, 12:03 AM #5
Re: Mitsubishi Mr.Slim heat pump
I understand but i saw from a Sanyo data sheet that the minimum the compressor would work is -25C so i am looking for such data but for the Mitsubishi, i have a installation manuel but it doesn't say.
A Sanyo service engineer told me some of is customers were heating at -20C.
-
01-01-2010, 01:07 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Mitsubishi Mr.Slim heat pump
.................................
-
01-01-2010, 01:30 AM #7
Re: Mitsubishi Mr.Slim heat pump
Big thanks man, its very nice and considerate of you.
-
01-01-2010, 03:51 PM #8
Re: Mitsubishi Mr.Slim heat pump
Ok what i'm thinking is to test it, check it very closely and give some feed back, i don't think just a few degrees less (2 or 3 C) should effect the machine but could do quite a difference in the house, i have a cottage and it manage to heat up the entire second floor and lately the weather went down to -13C and it shuts off at -10C.
Your tough?
-
01-01-2010, 05:41 PM #9
-
01-01-2010, 06:07 PM #10
-
01-01-2010, 06:24 PM #11
Re: Mitsubishi Mr.Slim heat pump
I am trying to find proof that making it work at a few degrees lower wont damage the outdoor unit.
Cause usually when it comes to degree control precision is not that precise, i don't think they would make it shut off at it's exact crucial point, they have to give a margin of error.
-
01-01-2010, 06:38 PM #12
Re: Mitsubishi Mr.Slim heat pump
Hey guys look at what i just found, take a look at the service manual.
It is the same for the 12k or 18k BTU
Why the Mitsubishi should be different, the 2 machines are pretty much the same.
us.sanyo.com/HVAC-Single-Split-Systems-Wall-Mounted-Heat-Pumps/Wall-Mounted-Heat-Pump-12KHS71
-
01-01-2010, 06:38 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-01-2010, 06:39 PM #14
Re: Mitsubishi Mr.Slim heat pump
Just put the www in front i cannot put url yet
-
01-01-2010, 06:40 PM #15
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
01-01-2010, 06:48 PM #16
-
01-01-2010, 06:52 PM #17
Re: Mitsubishi Mr.Slim heat pump
I have compare both very closely before a bought the Mitsubishi in the month of May 2009
-
01-01-2010, 07:05 PM #18
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Mitsubishi Mr.Slim heat pump
Ok, then you are saying that manufacturer intentionally forbid operation at much lower temperature.
What would be his reason to do that, and in same time other manufacturer reason to not do that?
And what specification tells you that they are same? Quote, please.Last edited by nike123; 01-01-2010 at 07:09 PM.
-
01-01-2010, 07:21 PM #19
Re: Mitsubishi Mr.Slim heat pump
-
01-01-2010, 07:44 PM #20
-
01-01-2010, 07:56 PM #21
Re: Mitsubishi Mr.Slim heat pump
-
01-01-2010, 08:16 PM #22
Re: Mitsubishi Mr.Slim heat pump
See guys i think that these days there is no mystery on how to make the best machine so they all make pretty much the same as they need to compete, same with cars and lots of other stuff.
I had also compare the fujitsu before buying and once again, pretty much the same
look here. but put the www in front
.ductless.ca/brochures/fujitsu/halcyon_06.pdf
Maybe i had my answer all along but wanted the personal experience of people?
-
01-01-2010, 08:27 PM #23
Re: Mitsubishi Mr.Slim heat pump
Like i said previously, i will test it an post feed back.
All i did is put the sensor inside the box instead of outside so temp. will not differ that much!
-
01-01-2010, 08:35 PM #24
Re: Mitsubishi Mr.Slim heat pump
Mitsubishi have recently brought out a product called Zubadan heat pump, here in the UK. This unit operates in heating with ambient temperatures up to -25c. I've not yet seen one or even heard of anyone that has purchased this system but it appears they have the technology in place. I can only find 7.1kW - 10kW on a selected Mr slim range. Go to products & choose Mr Slim on the Mitsi website: http://www.mitsubishi-aircon.co.uk/d...i_electric.asp
-
01-01-2010, 09:00 PM #25
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Mitsubishi Mr.Slim heat pump
Than what is the reason that Sanyo doesn't protect itself?
2-Print both specifications sheets and compare side by side.
What is your profession or area of expertize? How much you know about refrigeration and air conditioning?
You still did not quoted what data tells you that these two units perform same at low temperatures.
-
02-01-2010, 02:56 AM #26
Re: Mitsubishi Mr.Slim heat pump
I'll give you the way to know for certain:
1. Open the outdoor unit - gain access to the compressor;
2. Install a temp sensor 150mm from the compressor exit, on the discharge line (the hot one);
3. Let the unit pull down & watch the discharge temp;
4. If temp exceeds 107-110'C, then you are pushing your unit too far.
It is possible that the manufacturer lets the compressor discharge run up a little higher on non-continuous load, but not too much higher.
Let us know how you get on.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
02-01-2010, 03:37 AM #27
Re: Mitsubishi Mr.Slim heat pump
In NZ I think this call Hypercore, basically a larger outdoor unit on a smaller indoor unit, lots of smarts in the electronics (keep the refrigeration balanced)
I believe (not seen) that they flood the evap at low temps and have a heater in the suction line to ensure there is some level of superheat/and load.
They are marketted as the same heatput across a full temperature range (the sales guy tried to say the same COP across the whole range, Bull Sh** if you ask me)
Buzzant, there is no mystery in refrigeration principle, I agree, but how these are applied is the mystery, with slight changes in controls , air flow, coil(s) configuration you can change the working enverlope of a system. You design to achieve best results at the designers conditions. Different manufactures design around these different conditions. Just because the sanyo is rated to -25 does not make it better across the whole range.
( Not saying sanyo is good or bad, just not the same)
-
02-01-2010, 03:45 AM #28
-
02-01-2010, 03:50 AM #29
-
02-01-2010, 03:53 AM #30
Re: Mitsubishi Mr.Slim heat pump
Thanks MF.
Flashing off liquid carryover would either require a fairly hot heat source, or some sort of residence time... it takes a finite time & you'd need to be sure.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
02-01-2010, 07:53 AM #31
Re: Mitsubishi Mr.Slim heat pump
If there is anything I have learned over the years, its that people believe what they want to believe, simply because they want to believe it.
Yes... you had your answer all along, and thats the problem. Rather than let the evidence lead you to the answer, you let the answer lead you to the evidence. If you started with the opposite answer, you would find the opposite evidence. All roads lead to 'you are right'.Last edited by Gary; 02-01-2010 at 08:13 AM.
-
02-01-2010, 11:59 AM #32
-
02-01-2010, 12:22 PM #33
Re: Mitsubishi Mr.Slim heat pump
Before i buy i did print the specs. sheets of 3 different competitive heat pump and looked at them side by side to find that they all have pretty much the sames specs so!
Sorry mate but i am trying to clarify something, i'm not here to justify my self to frustrated people.
-
02-01-2010, 12:25 PM #34
Re: Mitsubishi Mr.Slim heat pump
Removed by desA...
Last edited by desA; 02-01-2010 at 12:54 PM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
02-01-2010, 12:25 PM #35
Re: Mitsubishi Mr.Slim heat pump
Sorry DesA i did not want to quote you on that one, my mistake.
it was met for Nick 123
-
02-01-2010, 12:45 PM #36
Re: Mitsubishi Mr.Slim heat pump
^ No problem... I'll remove my post above, then.
If you have a chance, try & measure the temperature I suggested. This will be useful for all of us.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
02-01-2010, 12:56 PM #37
-
02-01-2010, 02:12 PM #38
Re: Mitsubishi Mr.Slim heat pump
You know what guys?
I just put the sensor back where it belong and i am going to forget about it, i always like to push thing to their limit but if the risk of breaking it is to great it doesn't worth it, so i will live it be.
Thank you all for trying to help, peace out.
-
02-01-2010, 02:17 PM #39
Re: Mitsubishi Mr.Slim heat pump
^^ You cannot make a decision like that, without measuring the temperature.
As the other members have stated, each manufacturer sets up their systems differently. The difference between a reliable system & a blown compressor could be the few degrees you are wanting to over-run the spec by.
I simply would not take the chance, unless I was either experienced, or advised by the manufacturer...Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
02-01-2010, 02:27 PM #40
-
02-01-2010, 02:37 PM #41
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
02-01-2010, 04:08 PM #42
Re: Mitsubishi Mr.Slim heat pump
The Heat mode defost control stratagy has some impact on this minimum outside ambient temperature issue & different manufacturers deploy slightly differnt defrost stratagy.
For example
Mitsubishi Mr Slim split system heat pumps calculate an appropriate heat mode operation time untill the next defrost based on the lenght of time it took to complete the last defrost.
The minimum period of heating operation between defrosting is 20 mins when the last defrost took 15 min to complete.
If you look in the technical data books at the heating performance graphs you will see that at minus 10 - 12 deg C ambient the heat pump is doing arround 50 to 60 % heating duty only depending on other stuff like interconnect pipe length.
In practical terms as soon as the system starts heating mode in low abmient conditions the suction pressure is being reduced due to the frost forming on the outdoor coil. This makes the discharge temperature higher as the coil becomes more frosted.
At the Mitsubishi factories in Japan I know they do a lot of testing in environmental chambers.
So I would suspect that the Mitsubishi R&D engineers know that at minus 10 or minus 12 deg C the outdoor coil is going to be so heavily frosted within the minimum run time in heat mode that the compressor will be running at excessive discharge temp & will cause compressor damage.
Any way as stated before what is the point of a heat pump if it is in defrost for 15 mins & then heating at low heating performance for only 20 mins ?
In this case back up electric heating is needed.
Here in the UK we dont tend to get such extreem cold weather except in Scotland so this is not really any problem.
This is a global product & the manufacturer is only going to make a special design for very very low ambient conditions if there is a market & demand for such a product.
-
02-01-2010, 04:32 PM #43
-
04-01-2010, 10:59 PM #44
Similar Threads
-
New Heat Pump Forum
By Argus in forum Heat PumpsReplies: 17Last Post: 10-04-2010, 09:12 AM -
Sizing of Heat pump
By pinkpanther in forum Tools and CalculatorsReplies: 5Last Post: 24-05-2009, 08:16 PM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
commisioning mitsubishi heat pump boilers?
By northcool in forum Air ConditioningReplies: 2Last Post: 22-09-2008, 08:28 PM -
Will this heat pump work?
By goodguy in forum Heat PumpsReplies: 7Last Post: 08-03-2008, 04:14 PM