Page 3 of 4 FirstFirst 1234 LastLast
Results 101 to 150 of 166
  1. #101
    Apr 2001
    79
    5,071
    35
    Re: low high-side pressure, help
    Quote Originally Posted by mackking View Post
    no i didnt have a chance, but i would expect the pressure to rise since the refrigerant has nowhere to go, it would be compressed in the coil, hense the pressure should skyrocket.
    When you shut off the suction the compressor has nothing to pump into the high side... and the high side is still cooling off and draining off into the evaporator. If anything the high side pressure should drop.
  2. #102
    Apr 2001
    79
    5,071
    35
    the only other orifice i have is a .73, but when i installed it before it acted like it had too much restriction to flood the coil with enough refrigerant to keep it cool.
    Trust me, it will provide enough flow.
  3. #103
    Jun 2009
    florida
    77
    at this point i have nothin to loose so ill try the .73 again
  4. #104
    lebanon
    130
    hi
    ithink there is miss matching btw the comp&air handler unit it appear that u have a large air hanling unit condenser came with this small orifice should b too small to handle the load u can check the comp brand & serial #
  5. #105
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by tonyelian View Post
    hi
    I tend to agree about the mismatch. The evap seems oversized for the compressor, but then this could be simply an orifice mismatch.
    More worrisome is that the condenser seems oversized for the compressor.
    If the compressor is undersized (under-capacity) for both the evap and the cond, that probably means the compressor is inefficient.
    At this point I'm still hoping that the right sized orifice will show a good condenser load, but that may be just wishful thinking.
    As mackking says, at this point there is nothing to lose by trying another orifice.
  6. #106
    Jun 2009
    florida
    77
    i put in the .73, set it to 15f superheat but i still have a high pressure on the low side (85psi with a 66f suction line)
    the high side psi did rise but only to 225 psi. i couldnt get any more readings because it started pouring on me, but its still not bring the room temp down.
  7. #107
    Jun 2009
    florida
    77
    are u telling me that u think goodman installed the wrong compressor from the factory?
  8. #108
    Apr 2001
    79
    5,071
    35
    Any idea what the indoor and outdoor temps were at the time you took those readings?
  9. #109
    Apr 2001
    79
    5,071
    35
    No... an inefficient compressor is one with broken valves. The symptoms are the same as having an undersized compressor.
  10. #110
    Jun 2009
    florida
    77
    yeah the air in evap was 79 and the air out was 62, i know there is a good difference but it still dont seem cold enough to me.
  11. #111
    Jun 2009
    florida
    77
    how would i confirm an inefficient compressor
  12. #112
    Apr 2001
    79
    5,071
    35
    And what was the outdoor temp?
  13. #113
    Jun 2009
    florida
    77
    i couldnt check it at the time because of the rain but i thinkit was around 85
  14. #114
    Apr 2001
    79
    5,071
    35
    As the temp in the house comes down the superheat will drop, so you should remove some refrigerant to keep it up around 15F.
  15. #115
    Apr 2001
    79
    5,071
    35
    225 psi at 85F would be an improvement. There may be hope for this system yet.
  16. #116
    Jun 2009
    florida
    77
    there may be hope but it hasnt brought it down and shut off yet, do u think this is any indication of how its gonna perform?
  17. #117
    Mar 2007
    118
    I have to wonder if pix would help. There may be a surprise in store. It has happened with other threads.
  18. #118
    Jun 2009
    florida
    77
    what kind of pics do u want?
  19. #119
    Apr 2001
    79
    5,071
    35
    To get the charge just right, you need to adjust to 15F superheat when the house is down to your shutoff temp. We've been just ballparking it to compare orifices.
  20. #120
    Jun 2009
    florida
    77
    is the superheat effected by night time or daytime?
  21. #121
    Jun 2009
    florida
    77
    it just shut off!!
  22. #122
    Jun 2009
    florida
    77
    from 830 to 12 to drop it 8f
  23. #123
    Apr 2001
    79
    5,071
    35
    When it comes back on would be the best time to adjust the charge.
  24. #124
    Jun 2009
    florida
    77
    will the superheat skyrocket during the heat of the day? or should it stay pretty much the same?
  25. #125
    Apr 2001
    79
    5,071
    35
    The superheat will be higher when the house is warm.
  26. #126
    Apr 2001
    79
    5,071
    35
    You are not only cooling the air in your house... you are cooling everything in your house. And you are also dehumidifying everything. It has been very humid lately.
  27. #127
    Jun 2009
    florida
    77
    yeah i know
  28. #128
    Jun 2009
    florida
    77
    so far its holding 70f in the room, but it has been overcast and raining today too. so far so good
  29. #129
    Apr 2001
    79
    5,071
    35
    Got a full list of temps/pressures?
  30. #130
    Jun 2009
    florida
    77
    nope still rainin, but its running about 35-45 minutes during cycles
  31. #131
    Apr 2001
    79
    5,071
    35
    Did you trim the charge to 15F superheat?
  32. #132
    Jun 2009
    florida
    77
    i got in contact with goodman tesh support, they said the system required a .73 orifice(which i installed) and a superheat of 22f because uf the humidity. i did this yesterday and it has worked the best today but like i said it was overcast and raining. anyways here are the reading-
    suction temp=62f
    liquid line=83f
    condensor in=77f
    condensor out=88
    evap in=66
    evap out=53
    lowside=72psi
    highside=175psi
  33. #133
    Jun 2009
    florida
    77
    this was taken at 10pm and it was wet, 95% relative humidity
  34. #134
    Apr 2001
    79
    5,071
    35
    Low delta-T's... high suction... low head... I'm thinking this compressor is inefficient.
    The only other possibility would be a leaking reversing valve, but you checked the suction pressure on both sides of the reversing valve and they were identical.
  35. #135
    Apr 2001
    79
    5,071
    35
    I found a Goodman service manual:
    http://www.hvacpartsshop.com/asc%20series.pdf
  36. #136
    lebanon
    130
    hi
    ur air handler is 3.5 tons&condenser is 3 tons there is a miss match
    gary tanks for the link&the way u guide him
    i think every thing is clear now
  37. #137
    Apr 2001
    79
    5,071
    35
    The air handler is rated at 2.5 to 3.5 tons, based on 400CFM per ton. It is currently set on low speed (1000CFM) which should result in a low suction pressure... but the suction pressure is in fact high.
    One more thing we can try is to measure the temps of the two cold pipes at the reversing valve. If the valve is leaking across, the temp on the side towards the compressor will be considerably higher.
  38. #138
    Jun 2009
    florida
    77
    would a leaking reversing valve of an inefficient conpressor still pull a vacuum when the suction line is closed?
  39. #139
    Jun 2009
    florida
    77
    you asked if it would pull a vacuum, it did but it didnt do it fast and it wasnt much. ive seen systems with a clogged orifice and they would pull a hard hacuum very quickly.
  40. #140
    Jun 2009
    florida
    77
    also as a bit of info, the tech at goodman said he didnt think the highside pressure was low. but as im learning more of how the system works, it seems it would need a higher pressure to keep the refriderant from boiling in the liquid line, right?
  41. #141
    Apr 2001
    79
    5,071
    35
    Where are you measuring the evap air in and air out temps? Best would be at the air handler.
  42. #142
    Jun 2009
    florida
    77
    the return air is right above the air handler about 1ft and the closest out is at a vent 3ft away. its a downdraft.
  43. #143
    Jun 2009
    florida
    77
    i cant measure the out temp right from air handler because it mounts to the floor so i have to use the closest vent
  44. #144
    Apr 2001
    79
    5,071
    35
    3 ft away should be accurate.
  45. #145
    Apr 2001
    79
    5,071
    35
    Uhhh... No.
  46. #146
    Apr 2001
    79
    5,071
    35
    I would disagree. Generally the SCT is 20-35F above the temp of the air entering the condenser (20-35F TD), depending upon load and relative coil size. I have yet to see the TD hit 20F despite the high suction pressure.
  47. #147
    Jun 2009
    florida
    77
    Uhhh... No.
    in reading your post in a/c 101, you explained that the boilding of refrigerant in the evaporator removes the heat from the air(which i understand) but i also understood it to say by raising the pressure in the condensing coil it returned the refrigerant back to a liquid(by increasing pressure and removing the added heat) so i guess my question is, is the system raising the pressure enough to maintain the proper liquid state?
  48. #148
    Jun 2009
    florida
    77
    my next question is, by overcharging and having the wrong orifice, could that have damaged the valves in the compressor?
  49. #149
    Apr 2001
    79
    5,071
    35
    R22 at 175psi gives you a saturated condensing temp (SCT) of 93F. In order for the liquid in the liquid line to boil off, its temp would have to be higher than 93F. Its temp is 83F. Not going to happen... and since the two temps go up and down together, it can't happen.
  50. #150
    Apr 2001
    79
    5,071
    35
    Yes... it could.
  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Last Post: 19-07-2011, 03:16 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Last Post: 06-05-2009, 11:10 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Last Post: 10-03-2009, 01:03 PM
  4. High Pressure Freezing
    By mattynige in forum New Technologies
    Last Post: 19-06-2008, 02:03 PM
  5. discharge pressure too high
    By zahar in forum Trouble Shooting
    Last Post: 16-02-2008, 08:58 PM