    Hi guys i have been called to look at a Daikin 3MXS52E with three interior units off it. It has been installed for approx 10 months. An E6 error code has come up and i recently had the Daikin technician visit the property.
    He has put in down to moisture in the system and it is not a warranty issue.
    I would appreciate some info on the procedure of getting the moisture out of the system please.
    70
    4,702
    47
    Re: Moisture in system
    Quote Originally Posted by Debonair Spain View Post
    Erm! How long have you been an a/c engineer?
    Try a triple evacuation or deep vacuum search within the forum or google it!
    E6 Is listed in the details I have, as Outdoor Compressor lock / startup error
    or lock / over-current.
    Sounds to me as if there is an issue with the compressor!
    Mar 2006
    Merate (LC) - Italy
    2,549
    Daikin probably means "there was moisture in the system and now the compressor is f....d up". If this is the case, triple evacuation is no use and would not help restarting the compressor.
    Jul 2008
    London
    848
    Reclaim
    Vaccum x 3 with nitrogen triple vac etc
    Large 2 way HP drier in expansion line
    run for a day, change
    run for a week, change
    run for a month -change or remove
    How did he diagnose moisture anyway??
    May 2008
    spain
    54
    63
    Quote Originally Posted by multisync View Post
    Reclaim
    To be honest Multisync i have not had the chance to ask him as i have only just received the info from Daikin and now they are on holiday until Tuesday.
    But many thanks
    Split Croatia
    6,151
    But many thanks
    I would not do any recovery or drying of system before samples of oil and refrigerant are collected in manner that they are suitable for evidence and later analyze.
    If he did not measured moisture content and sampled oil, how he could tell that is not warranty covered?
    Also, moisture could be product of oil decomposition because high oil temperature and that could be because of some other fault in system, in which case that does not exclude warranty.
    May 2008
    spain
    54
    63
    Thanks Nike123 this is food for thought.
    Split Croatia
    6,151
    Another taught!
    If system is commissioned by authorized installer, then moisture in system cannot be reason for avoiding warranty repair since user is not responsible for faulty instalation.
  1. Troubleshooting for Daikin Aircon CTK25FVEN
    By JCTK in forum Air Conditioning
    Last Post: 05-06-2010, 07:18 PM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  3. How an expansion tank works?
    By Raadster in forum Fundamentals
    Last Post: 25-07-2008, 02:25 PM
  4. dakin e3 code
    By coolflow in forum Air Conditioning
    Last Post: 19-07-2008, 09:24 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Last Post: 15-05-2002, 06:19 AM