    airflow



    hie all.Still on commissioning .Im doing airflows for a new install heat pumps ducted systems.Im using a 4 " vane anemometer to get the velocities that correspond to the airflow needed at the supply registers.My formular is as below ,
    airflow =velocity * duct surface area
    velocity=airflow/duct surface area

    I will then adjust my blower speed to give me the velocity that corresponds to my desired airflow .

    Am I on the right track?
    Last edited by bangoman; 05-11-2008 at 01:14 PM.



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: airflow

    The higher the airflow, the higher the coil temperature, the higher the efficiency.

    On the other hand, the coil temperature must be low enough to achieve the desired humidity.

    Generally speaking, the coil leaving air temperature must be 20F/11K (or more) below the temperature at the thermostat.

    This can be demonstrated on a psychrometric chart:

    Find the desired room temperature along the bottom. draw a vertical line to where it intersects with the desired humidity. From there, draw a horizontal line to where it intersects with the 100% humidity line, then down vertically to find the needed leaving air/coil temperature.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: airflow

    Quote Originally Posted by bangoman View Post
    airflow =velocity * duct surface area
    velocity=airflow/duct surface area
    Airflow = velocity * duct free area

    If you are taking readings at the supply terminals be aware of the jetting effect caused by the terminal vanes or slots.

    Taking readings at the extract or air inlet terminals can sometimes be more accurate.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: airflow

    Airflow = Volume (m3/s, cuft/min etc)

    Volume = Velocity x Area

    Velocity = Volume/Area

    Area = Volume/Velocity

    Know any 2 you can find the 3rd.

  5. #5
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: airflow

    Brian ! by duct free area what do u mean ? wher do I find a duct free area that I can measure velocity
    Last edited by bangoman; 07-11-2008 at 09:41 AM.

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: airflow

    Quote Originally Posted by bangoman View Post
    Brian ! by duct free area what do u mean ? wher do I find a duct free area that I can measure velocity
    He means the cross sectional area of the duct.

    How accurate do you want your results because measuring the velocity at the grill/louver with just an anemometer is a bit "rough". You might try making a hood for the grill/louver but you should find a correction factor for that sort of thing.

    If you want to have confidence in your results I suggest you hire or buy the tools for the job (i.e. a balometer)

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: airflow

    Quote Originally Posted by bangoman View Post
    Brian ! by duct free area what do u mean ? wher do I find a duct free area that I can measure velocity
    Say you have a (metric) duct sized at 300 x 200mm with an air terminal at the end with 5 x 5mm bars across it.

    Duct area = 300 x 200 = 0.06 sq.m

    Five 5mm x 300 bars = 0.0075 sq.m

    Gross area = 0.06 sq.m
    Free area = 0.06 - 0.0075 = 0.0525sq.m

    If you measured a face velocity at the grille/terminal of 2m/s and used the duct gross area then t you would say that you had an air volume of 2 x 0.06 = 0.12 cu.m/s.

    In fact you should use the free area so the calculation goes 2m/s x 0.0525sq.m = 0.105cu.m/s and shortfall of 13%.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: airflow

    Brian and All thank u so much for the posts .Im becoming a better engineer evrytime .Thanxs again

  9. #9
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: airflow

    Hi all.We have a capture hood at work though its for bigger registers,is it ok if i fabricate an extension and use it on smaller registers .
    Last edited by bangoman; 11-11-2008 at 09:15 AM.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: airflow

    Yes, but be careful that you do not over-throttle the system.

    Too much resistance of the hood will give you false readings.

    If it is for only the odd job then you can make them from cardboard quite easily.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: airflow

    brian ,these are side wall registers nt ceiling ones .does it really matter.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: airflow

    Yes, it matters. Airflow is airflow, it doesn't matter where it's coming from
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Jan 2006
    Location
    Australia
    Age
    47
    Posts
    92
    Rep Power
    19

    Re: airflow

    thanxs brian just that my boss a work told me that the hood was only designed for the ceiling registers bt ddnt understand wat he meant by that

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: airflow

    Probably meant that you could reach the ceiling with the hood without needing ladders

    The proper way to make use of a hood is to compare the anemometer measured airflow rate with an accurate duct traverse measured airflow rate.

    This will give you a correction factor for the anemometer/hood and provide greater accuracy.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Air conditioning airflow
    By Third_techtrio in forum Air Conditioning
    Replies: 6
    Last Post: 28-11-2008, 11:55 AM
  2. Foster 1/3 Lack of airflow problem
    By Latte in forum The Trail of Tears
    Replies: 6
    Last Post: 14-08-2008, 11:49 AM
  3. airflow
    By tempered in forum Fundamentals
    Replies: 11
    Last Post: 20-01-2007, 11:39 PM
  4. A weird question about airflow measurement
    By Vincent Yu in forum Fundamentals
    Replies: 18
    Last Post: 16-10-2006, 10:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •