It is good piping design ?
Hello every body , i have a question have not been solved, i hope i will get the answer in this forum .my boss always design the refrigeration piping by putting the suction line and discharge line together ( two copper pipe touch each other ) with pipe insulation .Is this good for the evaporator superheat adjustment ? i read a lot of forum stated that good design has no need to adjust the TXV but if i am not adjust the TXV i will get high superheat at the compressor .( Example : piping for blast freezer ,120 feet long ).thanks for help !
-
12-10-2008, 03:12 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: It is good piping design ?
Some compressor manufacturers want superheat of 20K or more in low temperature applications. If we adjust that with TEV than evaporator will be inefficient. Therefore, it could be good to have some form of suction gas heat exchanger like in case when two pipes are together. You have better subcooling and better superheat in such case. Sometimes when that could not be achieved with pipes, you should install separate suction gas heat exchanger.
But if you have application as in air conditioning then such a superheat is bad for compressor then you should laid these pipes separately isolated.Last edited by nike123; 12-10-2008 at 04:09 PM.
-
12-10-2008, 03:59 PM #3
Re: It is good piping design ?
thanks for reply , i think i got the answer here .Beside that should i increase the superheat at the compressor to make the maximum capacity at the evaporator ?
-
12-10-2008, 04:17 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: It is good piping design ?
Maximum capacity at evaporator is when superheat is 0K!
You must maintain superheat at reasonably high level at which you are sure that there is no danger of liquid flood back to compressor in all working conditions, and at same time, low as possible to utilize evaporator surface as much as possible.
Check this!Last edited by nike123; 13-10-2008 at 08:00 AM.
-
12-10-2008, 04:35 PM #5
Re: It is good piping design ?
got it , i am going to do the observation before made any adjustment for that system . thanks
-
12-10-2008, 05:14 PM #6
Re: It is good piping design ?
Originally Posted by oilzee
I hope you mean the liquid line and NOT the discharge line.
The TXV controls the superheat of the evaporator. If you add heat to the suction vapor, The vapor temperature will increase. This results in a higher SUCTION superheat at the compressor. This can cause the compressor to overheat, which you do not want.
Originally Posted by [/FONT
That is a perfect example of where not to connect the liquid and suction lines. If you want subcooling use a separate mechanical subcooler, not the suciotn line.If all else fails, ask for help.
-
13-10-2008, 06:34 AM #7
Re: It is good piping design ?
I hope you mean the liquid line and NOT the discharge line.
Similar Threads
-
HVAC piping design software
By NoNickName in forum FundamentalsReplies: 26Last Post: 06-02-2010, 06:29 AM -
Piping Design Manual
By ErnieA in forum NH3Replies: 21Last Post: 16-06-2008, 08:51 PM -
Cooling tower piping design
By kaon in forum Technical SpeculationsReplies: 6Last Post: 24-01-2008, 07:00 AM -
A good Design?
By Servicefrigo in forum TrainingReplies: 2Last Post: 11-10-2005, 09:16 PM