Foster 1/3 Lack of airflow problem
Evening/Morning all,
Just thought i would share this one with you, may help out a less expreienced engineer who hasnt come across it before. I was asked by another angineer to go and have a look at a Foster 1/3 case where the opposite end to the evap, the cabinet temp was 6/7 degrees c higher than the return air at the coil.
Turned out the centre set of drawers had the incorrect size drawer in it so was blocking the air off and short cycling inside the unit. Hopefully you can see from the picture the drawer size difference. Not one i would expect to see often, obviously someones changed the drawers at some point and only put a low sided drawer on the top on of the first set.
Hope this makes sense.
Regards
Fatboy
-
24-07-2008, 02:13 AM #2
-
24-07-2008, 07:42 AM #3
Re: Foster 1/3 Lack of airflow problem
top spot,you really do have to be abit of everything for this trade,i will add detective
Paul
"KEEP IT COOL"
-
24-07-2008, 11:29 PM #4
-
13-08-2008, 12:31 PM #5
Re: Foster 1/3 Lack of airflow problem
Hi Ray, I dont suppose this site was in Northants was it???
-
13-08-2008, 10:02 PM #6
Re: Foster 1/3 Lack of airflow problem
Hi James,
Afraid not, It was out Aylesbury way in the middle of nowhere. Makes a change though, i seem to be spending most of my life in the NN/MK postcode area's at the moment. OH the joys of roundabout city
Regards
Fatboy
-
14-08-2008, 11:49 AM #7
Re: Foster 1/3 Lack of airflow problem
Phew! I had replaced the drawers on the same type of unit last month at a site in Northants, for one horrible moment i thought it was my doing! If there is a next time i will look out for that one. Cheers. ;0)
Similar Threads
-
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
York DXS45 capacity slide problem
By The Screwdoctor in forum Industrial CompressorsReplies: 8Last Post: 25-05-2010, 04:40 AM -
what's the problem
By botrous in forum Air ConditioningReplies: 35Last Post: 22-06-2008, 02:54 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
York Chiller Excessive Purges Problem
By imranmd in forum CommercialReplies: 5Last Post: 07-03-2008, 05:13 AM