    Mar 2008
    US
    Question Which factors will decide the temp and pressure in the end of condenser (before TXV)?
    The surface of cond? or TD of cond? Or compressor? Thanks.
    David
    Aug 2005
    5,302
    Re: Which factors will decide the temp and pressure in the end of condenser (before T
    Let's assume the condenser is air-cooled.
    Ambient air temperature + condenser TD = saturated condensing temperature (SCT). The SCT is the temperature of the liquid coming out of the condenser without subcooling. If the condenser is equipped/designed to provide sub-cooling then you have: SCT - subcooling = liquid feed temperature from condenser (this then flows into the receiver).
    If the receiver is exposed to air temperature greater than the sub-cooled liquid temperature then the liquid can warm up a little, hence causing a reduction in sub-cooling.
    If the liquid line is warmer than the surrounding ambient air temperature then the heat is rejected from the liquid line to the ambient air.
    Then, if the drier is clean the liquid arrives at the TXV as long as the liquid line pressure loss (or elevation increase) does not cause any subcooling effect to be lost.
    I think that covers the major items...
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    May 2008
    weston
    348
    US_Iceman is right as usual, but as for the pressure there are three main variables that affect it:
    The pumping capacity of the compressor makes the pressure of the condenser go up.
    The energy/time (heat) the condenser gives off reduces the refrigerant volume therefore lowering the pressure. This
    is affected by TD and surface and heat transfer coefficients (refrigerant, velocities, densities, cooling fluid
    temperature and density etc.)
    The amount of liquid leaving the condenser. If you flood the condenser you are definitely changing its pressure.
    Anything going on before the condenser is attenuated by the condenser so the pressure at the expansion valve (or any
    point in between) is condensing pressure minus the pressure drop you have caused by the flow of the liquid
    refrigerant from the condenser to that point.
    And as US_Iceman says, you may get a little more or less depending on heat gains/losses in between the condenser and
    where you measure.
    Am I doing their homework again, you think?
    Mar 2008
    US
    Quote Originally Posted by GXMPLX View Post
    Thank you Iceman and GXMPLX.
    Aug 2005
    5,302
    The energy/time (heat) the condenser gives off reduces the refrigerant volume therefore lowering the pressure. This is affected by TD and surface and heat transfer coefficients (refrigerant, velocities, densities, cooling fluid temperature and density etc.)
    Ahhh, now you are talking about transient or temporary conditions that occur outside of the normal design window. I was assuming clean condensers and everything designed properly.
    If this is homework then at least someone is asking good questions!
    GXMPLX's Avatar
    May 2008
    weston
    348
    No, no transient. The question asked wich factors affect, I simply mentioned in which direction it affects.
    Refrigerant pumped makes it go higher, reduction of volume due to condensation makes it go lower and of course the higher the mass flow you take out as liquid will also make it go lower, if you stop or reduce the out mass flow pressure will go higher like when you flood the condenser.
    These effects when combined can give a stable condensing pressure.
    Me too.
    The right questions yes, but you are givin' away the answers! As usual, you started it, ... I simply got carried away!
    Scotland
    327
    TD 15K Ambient 25C SCT= 37C ?
  1. Pressure Temp Charts
    By theapprentice in forum Tools and Calculators
    Last Post: 05-04-2008, 07:53 AM
  2. Compressor loading, cooling, and range of operation.
  3. temp / pressure relationship
    By wilks in forum Trouble Shooting
    Last Post: 27-09-2007, 08:21 PM
  4. Replies: 0
    Last Post: 28-08-2007, 09:48 AM
  5. oil dilution+high pressure and temp.
    By Dimitris in forum Technical Speculations
    Last Post: 27-04-2006, 11:00 AM