Re: Charging liquid through suction line?
I will describe how I do it when I charging thru low side.
If I know total amount, I charge by weight reading the amount drawn on scale and throttling on manifold valve.
I usually keep rate of charging by 2-5% (higher at beginning and lower at the end of charging process) of total charge in one minute, while watching that sight glass on my Refco 4 valve manifolds is not full of liquid (I keep sight glass with lots of bubbles). After 1/2 to 1 minute, I stop feeding refrigerant and wait for another minute or two that accumulated refrigerant (if any) evaporates. Then I start feed refrigerant again.
If I don't know total amount, I charge slowly, keeping sight glass on manifolds without liquid and interrupting frequently to check pressures. When they are near to be good, I look in scale and proceed with charging about 1-2% of total amount charged so far.
Now, I measuring subcooling, after some time system stabilize, and judging if it is more needed.
That is my way, which I adopted from my experience and after reading a lot of articles about proper charging methods. It works relatively fast and it is accurate and don't make any damage to system.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Liquid charging through the suction side
By deu58 in forum FundamentalsReplies: 13Last Post: 02-07-2010, 05:23 AM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM