    adding liquid refrigerant though low pressure side



    I understand that multi-component refrigerants such as r-404a must be charged into the system in liquid form. This can be accomplished rather easily whenever the system is in vaccum or with just a little charge on it. But what happens when the system already contains a good amount of charge? I know how difficult is to add liquid charge through the high side under this situation. A few years ago, I learned about a device designed to allow liquid charging through the low side without risking the compressor. I´ve been unable to find this device with the local suppliers. Does anyone of you would know how to fabricate a similar device, maybe with a capillay tube or expansion valve? Thank you



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: adding liquid refrigerant though low pressure side

    Or just throttle the liquid supply through your manifold gauges.
    Meaning regulate the liquid being fed into the low side by viewing it's flow through the sight glass.
    By means of opening and closing the supplied valve into the manifold.

    Be cautious though as remember you want the refrigerant to flash off in the sight glass before it enters the compressor.
    That way any glide becomes irrelevant as the refrigerant can't separate but is being fed into the compressor.
    Be careful though you have to monitor and control the flow.
    Grizzly
    Last edited by Grizzly; 10-06-2008 at 06:30 AM.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    What about using a heating tape around the cyilnder? That way you could easily warm the liquid up over the condensing temperature...

  4. #4
    Join Date
    Jun 2008
    Location
    NZ
    Age
    46
    Posts
    9
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    HI, you could use a reclaim unit to charge liquid into the receiver.

  5. #5
    Join Date
    Mar 2008
    Location
    AUSTRALIA
    Posts
    10
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    i dont think it would be a smart idea to heat a bottle up

  6. #6
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    66
    Posts
    78
    Rep Power
    21

    Re: adding liquid refrigerant though low pressure side

    Use a roll of copper pipe in between to heat it up you can easily see if going to fast just look at the frost or condens you will see on the pipe. if needed speed put it under water.
    if you fill complete bottle do not worry at all as everything will get into the system.
    and it will mix up again.
    computer shooter
    paul deelen
    +31653300739

  7. #7
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: adding liquid refrigerant though low pressure side

    If you are "trimming" the charge then do like grizzley suggests or you can buy a charging vessel with a manually adjusted orofice, to expand the liquid.

    If you need to put a lot in then in most cases pump the unit down then you can dump liquid straight in.(you might want to let it equalise for a while before restarting)

  8. #8
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: adding liquid refrigerant though low pressure side

    http://www.stridetool.com/tools/auto...access_01.html

    This link is one of those charging devices although different to the one I was thinking of.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by BUSHY View Post
    i dont think it would be a smart idea to heat a bottle up
    Why not? it is done a lot of the time.

    Specialist heater mats are used.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by TRASH101 View Post
    http://www.stridetool.com/tools/auto...access_01.html

    This link is one of those charging devices although different to the one I was thinking of.
    A little off-line with that option I think
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: adding liquid refrigerant though low pressure side

    I teach all my students to charge liquid by regulating the flow through the manifold valve, it has worked for me for too many years to admit and I have never damaged a compressor doing it.
    Sorry but I do not like the idea of heating the bottle to a temperature were all the component refrigerants in a zeotropic blend are in vapour state as you would have a bomb on your hands, as you raise the temperature you raise the pressure and evaporating temperature.

    Ian

    Ian

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Sorry, I didn't make myself clear. I didn't want you to heat the bottle over the critical point, but just above the condensing temperature.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    Sorry, I didn't make myself clear. I didn't want you to heat the bottle over the critical point, but just above the condensing temperature.
    Heating bottle only works with one component refrigerants.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by BUSHY View Post
    i dont think it would be a smart idea to heat a bottle up
    Why not? This is the fastest way but you have to know what you're doing of course. Like everything in our job.
    The high pressure will expand to the other side.
    We've charged big gas cylinders in packs/racks with 3/8 tube and heating them up with a roof burner.Even the paint on the bottle remains intact.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by coldkeeper1 View Post
    [ I´ve been unable to find this device with the local suppliers. Does anyone of you would know how to fabricate a similar device, maybe with a capillay tube or expansion valve? Thank you

    You could use a pressure coupling line fitted to your gauges to restrict the liquid while charging.
    Transvestites are men who like to eat, drink, and be Mary.

  16. #16
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: adding liquid refrigerant though low pressure side

    Hi Coldkeeper,

    Do you have access to 'ITE' tools in your location. They sell a flash charger which is what you want.

    http://www.ite-tools.com/

    You could try and make one using an inline sightglass, a small length of capillary tube and a couple of brass unions. Possibly use one end section from a copper pressure coupler. The short length of capillary ends just inside the sight glass and 'flashes off' the refrigerant....which you can see and monitor in the sightglass.
    Last edited by Electrocoolman; 12-06-2008 at 08:34 AM.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by nike123 View Post
    Heating bottle only works with one component refrigerants.
    Why?

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    Why?
    I should be more prcise. I meaned zeotropes, because of temperature glide.
    If you heat zeotrope mixture, than one component evaporate sooner then other and goes in to system, and other component stays in liquid phase and in charging cylinder.
    Therefore, you end up with changed composition of unknown characteristics in your system.

  19. #19
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Not true. If vapour is superheated more than the glide, you are evaporating all of the components.
    Poor zeotropes... they have such a bad reputation.

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    Not true. If vapour is superheated more than the glide, you are evaporating all of the components.
    Poor zeotropes... they have such a bad reputation.
    If you have liquid in drum you have saturated, not superheated refrigerant.
    At least, that is frequently said here!
    Also, every refrigerant manufacturer said that zeotropes should be charged in liquid state (stated at packing, or stamped on botle).

  21. #21
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Not true. Refrigerant must be charged in liquid state, but at any temperature.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    Not true.
    What is not true? That refrigerant in drum is not saturated therefore not superheated until it is liquid inside, or that every refrigerant manufacturer said that zeotropes should be charged in liquid state.
    I don't get what you are negating here!

    Refrigerant must be charged in liquid state, but at any temperature.
    Where in my posts I negate this? I only saying that zeotrope refrigerant should not be charged in gas phase, heated or not! My reasoning is stated in above posts.
    Did we got here some misunderstanding, because, for both of us, English is not native language?
    Last edited by nike123; 13-06-2008 at 08:00 AM.

  23. #23
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Actually my mistake. I've got little time to post and that doesn't allow me to answer properly.
    The cylinder can be heated so that it flows in the circuit more easily. It shall be charged in liquid phase, of course, not in gas phase, but as long as you charge all of the cylinder, it doesn't matter whether you charge liquid or vapour.

  24. #24
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: adding liquid refrigerant though low pressure side

    It's called a suction accumulator! And if pressure on the vessel is high you use recovery equipment with a suction acuumulator. This should not harm compressor as long as it doesn't overflow, so whatch it.

  25. #25
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by GXMPLX View Post
    It's called a suction accumulator! And if pressure on the vessel is high you use recovery equipment with a suction acuumulator. This should not harm compressor as long as it doesn't overflow, so whatch it.
    What are you talking about?

  26. #26
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: adding liquid refrigerant though low pressure side

    you get them at www dot emersonflowcontrols dot com, recovery equipment at www cpsproducts dot com

  27. #27
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by GXMPLX View Post
    you get them at www dot emersonflowcontrols dot com, recovery equipment at www cpsproducts dot com
    Let see if I understand your point.
    Do you mean that you use this when charging liquid in system? Also, you use it when recovering liquid from high side? Is that correct?

    P.S. I see that you are situated in UK , so language barrier should not be a problem. Try to be more descriptive. Mind reading is myth.
    Last edited by nike123; 14-06-2008 at 07:42 AM.

  28. #28
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: adding liquid refrigerant though low pressure side

    Read once this , written by the biggest French gas manufacturer http://www.climalife.dehon.com/do-re.../faq/show/id/1
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  29. #29
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by nike123 View Post
    Let see if I understand your point.
    Do you mean that you use this when charging liquid in system? Also, you use it when recovering liquid from high side? Is that correct?

    P.S. I see that you are situated in UK , so language barrier should not be a problem. Try to be more descriptive. Mind reading is myth.
    Noooou and Yup! I am not even near the UK but 6 time zones away (this explains my delays), language could be a problem mostly because of my &%$ spelling/typing mistakes! And English is a second language for me.
    You use equipment the way the manufacturer intends it to be used. If the system is in deep vacuum you first have to breake it letting liquid refrigerant in if you have zeotropic refrigerants and preferably charge full cylinders only (I'm assuming you cannot do this or vapour/liquid charging would not be a problem if you charge whole cylinders). Use the recovery to suck gas from the system (you have to make sure it is NOT taken from a place that mixture gas/liquid could occur, use the discharge valve of the compressor or condenser inlet (some systems could have more issues involved here) and NOT the receiver. Use places where it is in the right composition and use it to presurize the refrigerant cylinder (impossible to use a disposable one). On the outlet of the cylinder you have two choices, you either evaporate the liquid with your manifonld valve and make sure only vapour comes out using a sight glass (slow and requieres all your senses) or you use a suction accumulator between the cylinder and the system and you have your hands free to check the correct amount is being fed. If you are not sure the total amount has come out of the suction accumulator you have to use it like a precharged cylinder.

    "Also, you use it when recovering liquid from high side? Is that correct?"
    I'm not sure I get your point here I suppose you are asking if the same recovery eq. is used and that is a YES! I use CR700. If you refer to the suction accumulator, I use the cylinder with the recovery machine's suction to the gas valve and a connection to the liquid line of the system to the liquid valve of the cylinder so it acts like a suction accumulator.

    All this is described in the recovery equipment manufacturer's manual.
    And please don't hesitate to contact me directly if you disagree.

  30. #30
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: adding liquid refrigerant though low pressure side

    just an idea,

    make in copper pipe a spiral of approx 1mtr , a sight glass and 2 connections whit 2 small refrig tubes of 0.50 cm, both ends whit a valve, one end whit the manifold,so you have for about 2 mtr of charge.
    one end at the bottle and the other end at the LP side.

    close the LP side en open the bottle,when the tubes are filled, close the bottle en open the valve at the LP side, when needed you can heat up the copper pipe thill there is almost nothing left. close the LP side en start over till it is at the right point.

    it works for me to, its slow but accurate.


    Ice

  31. #31
    Join Date
    Jun 2007
    Location
    Kuwait
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by Grizzly View Post
    Or just throttle the liquid supply through your manifold gauges.
    Meaning regulate the liquid being fed into the low side by viewing it's flow through the sight glass.
    By means of opening and closing the supplied valve into the manifold.

    Be cautious though as remember you want the refrigerant to flash off in the sight glass before it enters the compressor.
    That way any glide becomes irrelevant as the refrigerant can't separate but is being fed into the compressor.
    Be careful though you have to monitor and control the flow.
    Grizzly
    I am using the same way for charging large tonnage chillers "Air cooled and Water cooled" for several years without any problems.

  32. #32
    Join Date
    Aug 2008
    Location
    MALAYSIA
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    r407c refill totally liquids.backward the refrigerant cylinder as follow the instruction at cylinder.

  33. #33
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    r407c cylinder does not have to be used upside down.

  34. #34
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    r407c cylinder does not have to be used upside down.
    That depends on cylinder. If cylinder haven't got pickup tube then it needs to be turned upside down.

  35. #35
    Join Date
    Jan 2004
    Location
    Queenstown, New Zealand
    Age
    48
    Posts
    18
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    Read through this thread and thought 'geez some poeple make life hard!' Easiest way is as stated, using manfold to flash off liquid so that vapour enters is the way to go.

    Heating of bottle should only be done by hot water or purpose made heater blanket/pad - direct flame not a smart idea!

    I remember the device original poster is talking about - they had one at college, from what I remeber it was a glass pot with an oriface in it, perhaps a bit delicate for most poeples work vehicles!

  36. #36
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by nike123 View Post
    That depends on cylinder. If cylinder haven't got pickup tube then it needs to be turned upside down.
    I wonder who is selling cylinders without the tube. Major suppliers do not require to put it upside down.

  37. #37
    Join Date
    Aug 2007
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    I have to agree with sighman, why are you people making things so difficult.

    The original post doesn't state what the size of the system is. Its pretty much down to common sense.... if you're throwing liquid into the suction/low side of a compressor thats 1HP and trying to kill it, well you might well succeed. I myself have never had any problems charging with liquid into the low side of a system providing you use your brain when doing it. That goes for domestics to 200HP packs.

    There used to be an adapter called "Quickcharge" that allowed you to use the vapour side of a bottle and it charged the system with liquid in small amounts. It came out when R134a first came on the scene.

  38. #38
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: adding liquid refrigerant though low pressure side

    Yeah, and the original poster is only 13 years old, so who cares.

    Someone read the article I mentioned? You can charge R407c in gaseous phase
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  39. #39
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by Porkington View Post
    There used to be an adapter called "Quickcharge" that allowed you to use the vapour side of a bottle and it charged the system with liquid in small amounts. It came out when R134a first came on the scene.
    And R134 isn't even a zeotrope, (begins with a '1')
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  40. #40
    Join Date
    Aug 2007
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: adding liquid refrigerant though low pressure side

    Yet it is a blended refrigerant which is why they suggested using the "Quickcharge". The fact that it isn't a zerotrope means f'all.

  41. #41
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by Peter_1 View Post
    Yeah, and the original poster is only 13 years old, so who cares.

    Someone read the article I mentioned? You can charge R407c in gaseous phase
    Yes you could but refrigerant need to leave gas cylinder in liquid phase!
    That article doesn't refer to charging of refrigerant. It refers to leaking of system.

    2 - A mixture with a high variation (for example R-407C) does not break down in a gaseous state in the presence of its liquid, or when it stops. In operation, the probability of a mixture breaking down is virtually nil.

  42. #42
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: adding liquid refrigerant though low pressure side

    Quote Originally Posted by NoNickName View Post
    I wonder who is selling cylinders without the tube. Major suppliers do not require to put it upside down.
    We have here few Chinese and Indian without pickup tube!

  43. #43
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: adding liquid refrigerant though low pressure side

    I am most bemused by this thread, though have read it with interest.

    If you have time to do it the way Grizzly said it would be the easiest and simplest of options. If you don't then you use a recovery machine.

    Isn't this obvious?

    If you don't have access to a recovery machine, the next most obvious choice is heating the bottle to give it positive pressure over the system being charged. Heating belts are readily available in most sales catalogues.

    All these other convoluted ideas (all be them good) are only necessary if you have to improvise to save time. Improvisation which would only be required due to a lack of forethought.

    GXMPLX, your written English is of a very high standard. Indeed, much better than that of many native speaking English. Your spelling mistakes are sparse (sometimes ony additions, like an e on the end of break) and only once did I read in your posts a semantic error that sounded a little French. Other than that I honestly thought you were English and in England.

    I wish I could write as well in my second language as you do!

    ps where's Weston then. I thought you were in a little village in Cornwall.
    Last edited by expat; 31-08-2008 at 04:32 PM.

  44. #44
    Join Date
    Apr 2008
    Location
    Kent
    Age
    41
    Posts
    68
    Rep Power
    17

    Re: adding liquid refrigerant though low pressure side

    whoah, I finally made it to the end of this thread! Just use your gauges! also I think the piece of kit your taling about is called a visi or vizi vapour. Its about the size of a drinks can and you can see the gas going in as liquid and flashing off.

  45. #45
    Join Date
    Apr 2008
    Location
    Kent
    Age
    41
    Posts
    68
    Rep Power
    17

    Re: adding liquid refrigerant though low pressure side

    found it on just****inggoogleit.com
    http://www.trutechtools.com/cart/ind...2cacc609bc4395

Similar Threads

  1. Liquid pressure amplification (LPA)
    By US Iceman in forum New Technologies
    Replies: 34
    Last Post: 10-02-2011, 10:01 PM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Vapour Pressure
    By Stev in forum Fundamentals
    Replies: 7
    Last Post: 18-03-2008, 09:48 AM
  4. Replies: 19
    Last Post: 30-01-2008, 10:20 PM
  5. High Side Pressure is ...
    By SULTAN in forum Trouble Shooting
    Replies: 5
    Last Post: 14-08-2007, 12:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •