21-09-2016, 07:38 AM #1
propylene refrigerant criteria
If we use propylene as refrigerant in the screw compressor,is there any criteria of the propylene refrigerant?If some chemical plant can provide propylene which purity is up to 95%,can I use the propylene as refrigerant?
-
21-09-2016, 09:06 AM #2
Re: propylene refrigerant criteria
.
See
http://www.boconline.co.uk/en/produc...e45-r1270.html
It is flammable
so be very carefull on how you use it.
Rob
... ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..
-
21-09-2016, 09:51 AM #3
Re: propylene refrigerant criteria
Propylene is used as refrigerant. I want to know the purity level and its effects.
-
21-09-2016, 10:20 AM #4
Re: propylene refrigerant criteria
It should be 100% pure.....
https://www.google.co.uk/url?sa=t&so...jelyRof3N6yxxA
Data sheet ^Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-09-2016, 11:32 AM #5
Re: propylene refrigerant criteria
If major impurity in propylene blend are propane (R290), 5% propane in propylene blend make small amount of glide - around 0.033 degree C ( 1MPa pressure and 19.48 degree C) and have none effect in practical use.
if dominate impurity are Ethane - it make more glide, much more than propane. In 1 MPa pressure, 5% ethane in propylene, dew-point 17.03 degree C and bubble point 13.23 degree C.
if you have choice, and don't can get pure >= 99.5% propylene, select propylene with propane as impurity before alternative propylene with methane as impurity
some welder fuel/MAP-gas have 99.5 % Propylene inside and 0.5% impurity in this blend are propane in most caseLast edited by xxargs; 21-09-2016 at 11:48 AM.
-
22-09-2016, 09:53 AM #6