    Sep 2017
    3
    404A Walk in freezer issue
    I've got a walk in freezer unit on board ship that's not coming down to temp. I've got 20 psi on the low side of the compressor, 280 on the high side. The comp/condenser is in the Engine Room where its about 110F. There's frost on the suction line and the sight glass is full. Any suggestions? Thanks!
    2,579
    29
    Re: 404A Walk in freezer issue
    Trevor,
    Pressures don't seem to bad, discharge a little high.
    Check all fans are going
    no ice on evaporator, should see all the way through with torch.
    No product in front of evaporator, good airflow
    door seal is sealing correctly.
    If you have a good thermometer measure air on/ off evaporator.
    Hot product put put in for some reason
    Sep 2017
    3
    19 F in, 18 F out. The box temp had gotten up to 32 but now is down to 27 F. I put a portable blower on the condenser after I blew out the coils with air. Evap coils are clean, no ice, good air flow. My walk in cooler is down (again)with a bad compressor so I'd cracked the freezer door a couple of inches and propped it open. We've done this on board a few times and the freezer unit has always maintained 20-25 F while keeping the cooler mid 40's. I'm off the coast of Thirdworldistan for a couple days until we go into port and I'm trying to keep the little food in the cooler from spoiling.
    Thanks for the reply Ranger1
    Feb 2009
    telford
    2,068
    27
    Off the coast of where?
    Sep 2017
    3
    Trinidad...
    Sep 2009
    Cyprus
    71
    10
    Check your air flow through the evaporator or icing. Indications are that the evaporator is frozen solid.
    On normal conditions you can not have a room temperature of 27F and air in to evaporator 19F.