Results 1 to 9 of 9
    Nov 2010
    Wirral
    28
    4
    Isolare circuit via controller
    Hey guys,
    We have just took on a new site which has two carrier chillers running on Pro Dialog Plus controllers. They are not in a good condition atall. I have found a leak on 3 seperate circuits, 1 compressor faulty, 2 condencer fans tripped, the frame work is all rusted and the chiller with the faulty comp was completly isolated including water valves.
    My question is there a way to isolate circuit A via the controller and keep circuit B & C running?
    Sep 2010
    69
    209
    10
    Re: Isolare circuit via controller
    You haven't said which model chiller it is.
    Manuals for the chiller and controller can be downloaded from here...
    http://eto.carrier.com/lit2.asp
    Brian, retired in Devon.
    Nov 2010
    Wirral
    28
    4
    Quote Originally Posted by FaultCode View Post
    30RB802PT023/303
    Thanks i will look over that link
    Nov 2010
    Wirral
    28
    4
    I found the manual via the link you provided but it doesn't state how to disable a circuit.
    Mar 2005
    u.a.e
    166
    13
    Let turn off compressor breakers of circuit A, It will create alarm for this circuit , Chiller may run with partial load with remaining circuits. Also you have to isolate compressors by removing power supply wires, Control wires oil heaters and insulate them before to work on it.
    Take care when working with Electricals and think twice before to do any alteration.
    Nov 2010
    Wirral
    28
    4
    Quote Originally Posted by malik55 View Post
    Test before touch. I always treat conductors as live.
    I cant have the chiller in fault as it sends out the fault to the call center.
    Mar 2005
    u.a.e
    166
    13
    Normally there are individually alarm relays for each circuit , which can be disconnected so Alarm may not forward to center, but if you have CCN system then I think is not possible to isolate by hardware means.
    Feb 2012
    Ru
    38
    13
    The easiest way to put this compressors out of operation is to disconnect some pressure transducer connector. For example discharge transducer
    Mar 2005
    u.a.e
    166
    13
    If you have to work on the compressors you need to isolate completely and not only by disconnected a transducer or a sensor.