Results 1 to 8 of 8
    Jun 2014
    india
    High discharge with air
    Hi friends I want to know reciprocating compressor running with high discharge pressure in plant have air ? and what effects plant when plant in air
    Sep 2009
    Iran
    483
    12
    Re: High discharge with air
    when you have air in system
    your discharge temperature and pressure is high
    so your lubrication in compressor is become poor and also you have more pressure and you spend more power and your efficiency comes down .
    Jun 2014
    india
    Quote Originally Posted by mbc View Post
    Thank you MBC my plant discharge pressure is 235 PSI in 30 PSI suction pressure condensing temperature is 34 ' c that is normal ?
    Sep 2009
    Iran
    483
    12
    what is the your refrigerant in the system?
    Jun 2014
    india
    Ammonia refrigerant reciprocating compressor 235 tr 6 cylinders 750 rpm
    Sep 2008
    Canada
    776
    12
    At condensing temperature of 34C your condensing pressure should be around 180 psig. How did you measure condensing temperature?
    2,579
    29
    Could be a few things need checking
    - air in system
    - water sprays blocked, poor water distribution, dirty strainers.
    - water pump not performing
    - build up of scale or calcium on comdenser tubes
    - fans not working correctly. direction, air bypass, missing
    - condenser to small or mis-matched
    - system overcharged with refrigerant, receiver should never be over 80% full
    The pressures you have are possibly close to relief valve setting, what are they set to relieve at & what is compressor high pressure switch set to, it should be below relief valves 10 to 15%.
    Jun 2014
    india
    Thank you so much