    How much oil will be needed when replacing Coalescing filter on a RWB II 60.
    Thanks
  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    2,482
    Rep Power
    27
    Re: Frick RWB II Coalescing filter
    http://www.johnsoncontrols.com/-/med...ick_rwf_ii.pdf
    Page 7 & 27 may be of use.
    See torque setting on coalescer filter but on 27
  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    2,482
    Rep Power
    27
    WYLBEK,
    From what I can gather 25 gallons oil separator & 3.5 oil cooler.
  4. #4
    Join Date
    Nov 2016
    Location
    United States
    Posts
    2
    Rep Power
    0
    Thanks Ranger1, I looked up in manual that it holds 35 gallons in machine, but wasn't sure on how much would be in system elsewhere. 25gallons sounds good to me.
  5. #5
    Join Date
    Jun 2011
    Location
    Australia
    Age
    38
    Posts
    302
    Rep Power
    15
    Hey,
    Don't forget - the Coalescor is on the weir (dry) side of the separator baffle..
    Replacement of the Coalescor should not be impacted by oil in the separator.
    Happy tinkering
    Mankind does not know why Coffee make us poop..
    https://m.youtube.com/watch?v=U8Fqyyv16SM
  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    2,482
    Rep Power
    27
    Quote Originally Posted by HVACRsaurus View Post
    Hey,
    Happy tinkering
    Normally we would just change coalescer, Frick recommend change oil as well, because it is a fine filter I guess they want the best for new filters.