Results 1 to 2 of 2
    Jan 2017
    Australia
    27
    1
    Exclamation Cool room unit freezing up
    hi everyone, hope you can help us solve our problem
    Problem air con unit element is freezing up solid ice, over 30deg days only and fine in winter
    specs
    room size L2.1 x W1.2 x H2 meters with 75mm insulated freezer walls , all joins and sealed inside
    air con 1.6kw specs http://www.kelvinator.com.au/Product?model=KWH15CME
    basic controller unit for air con turn on and off 1-4deg
    unit located inside side with door open but no sun hit unit
    used store meat inside
    freezing multiple times today, out side temp 40.7
    air con temp sensor located at element, controls unit
    in middle room at 1deg is 0.5+ and at 4deg is 2+
    takes 3 hours from 4 to 1 and 10min 4 to 1
    tried opening the recirculation vent a little try help defrosting but then take ages cool room
    https://postimg.org/image/pyr6re90t
    https://postimg.org/image/pn9qemskt
    here's our weather
    39.7C rising
    Dew Point
    6.1C falling
    Feels Like
    37.2C
    Relative Humidity
    13%
    Wind
    icon
    WNW 18km/h rising
    Wind Gusts
    28km/h
    Pressure
    1001.1hPa
    cheers
    Oct 2001
    Nottingham UK
    5,127
    42
    Re: Cool room unit freezing up
    So, let me get this right....you are trying to use a window rattler for a chill room with a required temperature of 1C to 4C and you can't understand why the evaporator is freezing up?
    I'm back on the Pale