    May 2016
    Cairo
    31
    1
    Lightbulb YAEB millennium recip chiller
    Hi guys
    my chiller model is (YAEP99XD9B50PA) and I want to know how to change the set point of the oil temperature
    because it's too high and the heater can't reach that set point
    3,356
    Re: YAEB millennium recip chiller
    Quote Originally Posted by Eng Amgad Gamil View Post
    Hi guys
    Do you mean compressor sump heater thermostat?
    Can you let us know it's current setpoint & what temperature it get's up to now.
    ireland
    1,450
    41
    If i remember right, the setpoint is floating, i think it needs to reach 10degrees above ambient. Check your ambient sensor is correct and then check that the heater is working properly.
    Somerset
    69
    4,698
    Al is spot on!
    Unless the controller see's a oil temp of 10c above the ambient reading.
    The controller will assume that refrigerant is present and as a safety feature lock the chiller out on low oil temp.
    If the chiller is in a room which has a ambient higher (10c) than the standing Oil Temp you will be locked out.
    Stick a wet rag over the ambient probe if the above applies. To lower the ambient to oil ratio.