    May 2008
    uae
    44
    40
    carrier 30gx chiller EXV problem
    Dear all.
    we have a carrier 30gx chiller its expansion valve is not opening,we try through test its opening .but in normal condition its not working please help me to fix this
    Oct 2009
    Norway
    Re: carrier 30gx chiller EXV problem
    Have you checked if the low pressure transducer and superheat probe is showing correct values?
    May 2008
    uae
    44
    40
    suction pressure and superheat are showing actual values
    3,355
    Oct 2009
    Norway
    How did you test the exv?
    the water inlet/outlet probes are also showing correct values?
    Is there a seperate fuse for the exv?
    Have you checked the sub menu that the exv is requesting opening and measured the signal given to the exv?